Freezer runs all time lost most of what was in it. temp was 34Degs. Taped lines added freon 134a, LS runs 3-4 psi HS run 320 psi. Name tag calls for 140 psi LS and 320 psi HS. Current draw is 1.8 amps for compressor model plate calls for 5 amps After adding freon it will pull down to 16 degs. I am thinking restriction if dryer or cap tube. Any thoughts would be welcome
Thanks John
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 9/10/2007(UTC) Posts: 9,586
Was thanked: 2 time(s) in 2 post(s)
|
You most probably have a evaporator refrigerant leak, or a bad compressor. Pressure readings on low side way too high. The pressure numbers on the name tag are test pressures, not running pressures. For a modern compressor, your compressor current is too high, probably from non-compresable air in the system. Partially clogged capillary rare and would show up as a low current draw.
|
|
|
|
Rank: Member
Groups: Registered
Joined: 6/21/2010(UTC) Posts: 4
|
Richappy
Thanks for your reply I would like to ask some questions if its ok.
1. What should the low side run? 2. After adding freon why did it not start to freeze? 3. Are the newer freezers running less than 200 watts? 4. How can I determine iff the compressor is bad?
I am very confused. Trying to look at this in a logical way I can add freon until the discharge preasure will run will run up to 400 psi and will draw a little over 3 amps the side of the freezer will get so hot you cannot tuuch it. At this point it will still not pull down below 16 degs F. I can remove the shield from the evoperator it will frost up, and probably freeze. In my minds eye I can't see enough liquid going through the capillary.
Thanks for your help all comments welcome.
John
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 9/10/2007(UTC) Posts: 9,586
Was thanked: 2 time(s) in 2 post(s)
|
All pressure/performance indicates a weak and leaky compressor, should pull down the freezer below zero. Normal low side compressor should be around 4 to 6 pounds per pressure temperature charts for R134A. if forced air evaporator defrosts it, not a good sign.
|
|
|
|
Rank: Member
Groups: Registered
Joined: 6/21/2010(UTC) Posts: 4
|
Thanks
I know that I will need to replace this freezer, and that is the plan.
I am not questioning your responce or knowelge just trying to get a better understanding of what is going on. I know now that the PSI's listed are for leak tests. I know now that the normal discharge psi is 175 - 200 and the suction psi is from 3-5 psi. At this point in my minds eye there should be enough liquid passing through the dryer and capillary tube to reach the heat exchange/evoperator boil off at -16 deg F and go through its normal temp rise (on home ac is about 20 degs) not sure here probably 3-4 degs to be compressed again and condense to liguid in the condenser and give up the acculated heat. I am babling now due to my confused state. I have a question the point of measuring the discharge psi shows around 45-55 degs C , should this warm to the touch and cool due to room temp?
Thanks John
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 9/10/2007(UTC) Posts: 9,586
Was thanked: 2 time(s) in 2 post(s)
|
A cool discharge is due either to a weak compressor, or air contamination, or just lack of refrigerant.
|
|
|
|
Rank: Member
Groups: Registered
Joined: 6/21/2010(UTC) Posts: 4
|
Thanks for the reply
Can you direct me to a web site to where I can gain some insite on compressors?
I can't understand a copmressor that will build a discharge psi of 400 psi as weak. I can understand that I may have got air in the system. When I look back on your original though on the problem you stated leak in the evoperator that makes sense because there is a spot on the tile flour that will not wash clean. So there must be some reaction between the compressor oil and the tile. This ment nothing to me in the begaining. So low refrigerant must have been to original problem after 10-11 years of service, or the freon I added was not the same my came for autozone designed for vehicle a/c systems. If it is a restricted capillary I would not change the evoperator because it is part of the capillary/heat exchange.
Thanks again for responding to request for help
John 423 653 8899
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 9/10/2007(UTC) Posts: 9,586
Was thanked: 2 time(s) in 2 post(s)
|
You can do a google search for info.
|
|
|
|
Forum Jump
You can post new topics in this forum.
You can reply to topics in this forum.
You can delete your posts in this forum.
You can edit your posts in this forum.
You cannot create polls in this forum.
You can vote in polls in this forum.
Important Information:
The AppliancePartsPros.com uses cookies. By continuing to browse this site, you are agreeing to our use of cookies.
More Details
Close