It's a Tappan furnace, model L1RC 080D-16B, serial #- L1D060606846.
I've checked the inlet and the outlet, though both seam fine. I pulled the output line and there seamed like there was a lot of condensation, though I'm not sure if that is a norm. Runs fine otherwise. I don't think the limit switch is bad-since the motor is hot to the touch. The unit did freeze up this summer while running the ac, would that cause excess water and make the motor run harder? I'm not sure were to go from here. Any ideas?
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 9/1/2008(UTC) Posts: 440
|
Originally Posted by: jmag I've checked the inlet and the outlet, though both seam fine. I pulled the output line and there seamed like there was a lot of condensation, though I'm not sure if that is a norm. Runs fine otherwise. I don't think the limit switch is bad-since the motor is hot to the touch. The unit did freeze up this summer while running the ac, would that cause excess water and make the motor run harder? I'm not sure were to go from here. Any ideas? A complete make, model number, and serial number of the unit is necessary. The information is extremly neccessary.
|
|
|
|
Rank: Member
Groups: Registered
Joined: 7/9/2010(UTC) Posts: 4
|
It's a Tappan furnace, model L1RC 080D-16B, serial #- L1D060606846.
I've checked the inlet and the outlet, though both seam fine. I pulled the output line and there seamed like there was a lot of condensation, though I'm not sure if that is a norm. Runs fine otherwise. I don't think the limit switch is bad-since the motor is hot to the touch. The unit did freeze up this summer while running the ac, would that cause excess water and make the motor run harder? I'm not sure were to go from here. Any ideas?
|
|
|
|
Rank: Member
Groups: Registered
Joined: 7/9/2010(UTC) Posts: 4
|
While still under warranty, a service person came out and found a kink in the condensate line that comes out of the side (kink was from the original install). Witch caused the original over heat 3 Yrs ago. So I took apart all condinsate lines that I could track and blow/sucked them out, via air compressor/shop vac. The switch does not pop anymore, though the motor still seems hot. I looked at the "fan" there does not appear to be a pug to serve as a drain of sorts under the unit. There is an 1" x 3/4" piece of plastic that may serve as one, though I do not see any kind of release, there is a 1/8 hole in the center of the piece that I cannot quite see what it goes to, there is a mounting screw next to said piece, so I don't think it's a mount.........?????
|
|
|
|
Forum Jump
You can post new topics in this forum.
You can reply to topics in this forum.
You can delete your posts in this forum.
You can edit your posts in this forum.
You cannot create polls in this forum.
You can vote in polls in this forum.
Important Information:
The AppliancePartsPros.com uses cookies. By continuing to browse this site, you are agreeing to our use of cookies.
More Details
Close