I found that my compressor was low on r134 (negative pressure). After searching the internet for the correct pressure, I found all kinds of pressures, ranging from 55psi (I finally decided was for automotive or a/c, even though claimed to be for a refrigerator) to a more reasonable 3 to 5 psi. As my compressor was made by Whirlpool, one pundit said it should be on the lower number, ie 3psi.
I have used this number, but my technical information manual, says 0psi. Experimentation seems to indicate 0psi doesn't cool very good, so I am using 3psi, which gives me a little frost on the suction line (can't see any frost on the evaporator).

My unit now cools to freezer 0 degrees and refrigerator 40 degrees, but requires the control to be turned up (cooler) higher than in the past. Could the compressor also be weak?
Sponsor
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
richappy  
#2 Posted : Monday, August 12, 2013 3:19:20 AM(UTC)
richappy

Rank: Advanced Member

Groups: Senior Expert
Joined: 9/10/2007(UTC)
Posts: 9,586

Was thanked: 2 time(s) in 2 post(s)
If you get frost up to the compressor, the system is over charged.
If your low side pressure was not below -20 pounds, you have a bad compressor. Fridg. will run a lot and waste power.
darth  
#3 Posted : Monday, August 19, 2013 12:03:06 PM(UTC)
darth

Rank: Member

Groups: Registered
Joined: 8/24/2008(UTC)
Posts: 27

Even 2psi frosts the tube to the compressor. I'll try lowering to 1psi.
Marat  
#4 Posted : Thursday, January 23, 2014 10:21:11 AM(UTC)
Marat

Rank: Member

Groups: Registered
Joined: 1/23/2014(UTC)
Posts: 7

richappy  
#5 Posted : Saturday, February 1, 2014 8:49:33 AM(UTC)
richappy

Rank: Advanced Member

Groups: Senior Expert
Joined: 9/10/2007(UTC)
Posts: 9,586

Was thanked: 2 time(s) in 2 post(s)
If you have heavy frost in the freezer coils, the system will run too cold and the R134A vs temp chart will indicate a lower pressure, best to clean coils first.