The thermostat calls for heat, the furnace lights but when the fan switch should start the blower, the furnace hi-temps (shuts the gas valve off) then the blower starts after about 2 1/2 minutes. Soon the gas valve relights the burners and all runs well...What should I be looking for?

Thank you!
Sponsor
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
whsydddy9  
#2 Posted : Wednesday, October 27, 2010 4:16:53 PM(UTC)
whsydddy9

Rank: Member

Groups: Registered
Joined: 10/18/2010(UTC)
Posts: 41

I replaced the Camstat with a fan switch w/ safety...works fine now!:eek: