On the Whirlpool WRT316SFDM01, I would not chase a thermistor yet. This model uses a mechanical temperature-control thermostat, WPW10511937, for normal temperature control. Coast Parts
The important clue is that the compressor actually starts, runs about 30 seconds, then shuts off, while both fans continue running. That points much more strongly toward the compressor/start circuit than a temperature-control problem.
What I would check next
The compressor start components on this model are:
- Start device/overload: WPW10448874 — which you’ve already replaced. Whirlpool Parts
- Run capacitor: WPW10662129 — this attaches to the start device and should also be checked. Whirlpool Parts
Also, don’t put much weight on the new start device rattling. A rattle by itself isn’t a reliable test of this type of start device.
The quickest useful test now is at the compressor terminals. Unplug the refrigerator, remove the start device, and you’ll see the three compressor pins. Measure resistance between all three combinations:
Pin 1 → Pin 2
Pin 1 → Pin 3
Pin 2 → Pin 3
You should get resistance on all three combinations. The two lower readings added together should approximately equal the highest reading.
Then check each individual compressor pin to the bare metal compressor shell. You should get OL/infinite resistance on all three. If any compressor terminal has continuity to the compressor shell, the compressor is electrically shorted and is bad.
One test that would tell us a lot
When it shuts off after approximately 30 seconds, listen right at the compressor/start device.
If you hear a distinct click, and then several minutes later another click followed by another attempt to start, the compressor overload is opening. With a new correct start device installed, that usually leaves:
1. A bad run capacitor, or
2. A compressor that is mechanically tight/locked or drawing excessive amperage.
The fact that the compressor isn’t hot doesn’t rule this out. If it’s only running 20–30 seconds before the overload opens, it may not have had enough time for the compressor shell to become noticeably hot.
If you have a clamp amp meter, an amp reading on the compressor common wire during those 30 seconds would be especially helpful. A compressor that shoots to a high current and then trips the overload strongly indicates a compressor problem.
Since the evaporator and condenser fans are operating and the compressor is being commanded on, I would not replace the thermostat or go looking for a thermistor at this point. The thermostat is clearly calling for cooling if the compressor is being energized.
If you give me the three resistance readings between the compressor pins (for example, 3.2Ω, 5.1Ω, 8.3Ω), I can tell you whether the compressor windings look normal before you buy anything else.