clydeself  
#1 Posted : Monday, April 21, 2014 12:49:46 PM(UTC)
clydeself

Rank: Member

Groups: Registered
Joined: 9/7/2012(UTC)
Posts: 14

The compressor is warm to the touch and vibrating. The fan is running and the coils are clean. The freezer is cool, but is not freezing things. I have adjusted the thermostat and it does not make a difference. The door seal is not broken anywhere either. There is one place on the back wall of the freezer that has ice on it. The rest of the freezer has no ice anywhere on the walls. The fan inside the freezer is also running. What would you check?
Sponsor
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
denman  
#2 Posted : Tuesday, April 22, 2014 4:49:00 AM(UTC)
denman

Rank: Advanced Member

Groups: Senior Expert
Joined: 2/29/2008(UTC)
Posts: 19,638

Thanks: 1 times
Was thanked: 11 time(s) in 11 post(s)
Here are your parts
Parts for Frigidaire FRS26R2AW5 Refrigerator - AppliancePartsPros.com

I am assuming that the compressor runs continuously other than when the unit goes through a defrost cycle.

Remove the rear cover in the freezer so you can inspect the defrost coils.

If they are heavily iced/frosted over you have a defrost problem.
It should be fixable for a reasonable cost

If there is only frost in one area (usually where the freon enters the coils) then it is a sealed system problem. This would be an expensive repair as you need a pro. Often it makes more sense to put the dollars toward a new unit.

Be sure to do the check after the compressor has run for an hour or so. If you check it shortly after a defrost cycle then you could reach the wrong conclusion.

Below is a link. Take a look at the example pictures about half way down the page.
http://www.applianceaid.com/ref...ator-not-cold-enough.php
THIS FORUM IS DEAD!!!!!!!
clydeself  
#3 Posted : Tuesday, April 22, 2014 9:11:50 PM(UTC)
clydeself

Rank: Member

Groups: Registered
Joined: 9/7/2012(UTC)
Posts: 14

Took cover off and found ice on one end. Did not hear the compressor or the fan running so waited until I heard them running for couple of hours. Took panel off again and found less ice than before. Left panel off to watch over next 24 hours. Appears to be internal system and would require a pro. What do you think?
clydeself attached the following image(s):
P_20140422_221218.jpg
denman  
#4 Posted : Wednesday, April 23, 2014 9:53:46 AM(UTC)
denman

Rank: Advanced Member

Groups: Senior Expert
Joined: 2/29/2008(UTC)
Posts: 19,638

Thanks: 1 times
Was thanked: 11 time(s) in 11 post(s)
Perhaps it is just the angle of the picture but the defrost heater does not seem to be in the correct position. Looks like it is not parallel with the back of the freezer and I think it should be.

When you first opened it up you may have been in a defrost cycle and that is why the compressor and fans were off.

The ice at the top does look like a sealed system problem but I would try to confirm this.
Unplug the unit, take a hair dryer and melt off all the ice at the top. Just be careful that it does not overflow the drip pan under the unit.Perhaps mopping some of it up will help.

Then put the cover back on and let it run for an hour or so and reinspect the coils.

If there is frost just at the top of the coils then I would say it is a sealed system problem.
It will be an expensive repair and often it makes more sense to put the dollars toward a new unit.
THIS FORUM IS DEAD!!!!!!!
clydeself  
#5 Posted : Thursday, April 24, 2014 7:16:39 AM(UTC)
clydeself

Rank: Member

Groups: Registered
Joined: 9/7/2012(UTC)
Posts: 14

I defrosted the coil with a hair dryer and got rid of all the ice. After one hour, there was ice at the front end. After 11 hours there was only a small increase.
clydeself attached the following image(s):
P_20140423_223908.jpg
P_20140423_235501.jpg
P_20140424_105439.jpg
denman  
#6 Posted : Thursday, April 24, 2014 8:20:17 AM(UTC)
denman

Rank: Advanced Member

Groups: Senior Expert
Joined: 2/29/2008(UTC)
Posts: 19,638

Thanks: 1 times
Was thanked: 11 time(s) in 11 post(s)
I would say this is a sealed system problem and will be an expensive repair.
THIS FORUM IS DEAD!!!!!!!
clydeself  
#7 Posted : Thursday, April 24, 2014 9:14:40 AM(UTC)
clydeself

Rank: Member

Groups: Registered
Joined: 9/7/2012(UTC)
Posts: 14

Thank you so much for your time and advice. We will go today and begin or search for a new one.
denman  
#8 Posted : Thursday, April 24, 2014 1:51:58 PM(UTC)
denman

Rank: Advanced Member

Groups: Senior Expert
Joined: 2/29/2008(UTC)
Posts: 19,638

Thanks: 1 times
Was thanked: 11 time(s) in 11 post(s)
You are welcome.

Just too bad the end result was not better.