Dear Appliance Repair People: My refrig often freezes veggies (28 deg F), often is too warm (48 deg F). Freezer varies from OK (0 deg F) to a bit warm (very soft ice cream). Often refrig is OK, but freezer too warm even with it set to max cold (#5). Often have water in bottom of refrig--probably from freezer. I suspected the cooling thermostat & VERY carefully cleaned part of it & that helped the irratic behavior; but now it's out of adjustment. How do I set the "cut in" and "cut out" screw adjustments?. Or, if I simply replace this part, will that fix it, or is it some other temperature controller part? Thanks for your interest. --David
|
|
|
|
Rank: Member
Groups: Registered
Joined: 10/12/2008(UTC) Posts: 4
|
:confused: Not sure why I received no response to my earlier post. The latest is that the refrig now seems to cool OK in the Frig section (36-40 deg), although Freezer is always a bit warm (very soft ice cream). Periodically (maybe once or twice a day) everything thaws out way too much, and then it starts cooling again. Is this perhaps a problem with the defrost timer or another part of the defrost system?
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 5/28/2008(UTC) Posts: 1,620
|
You could have a defective defrost termination thermostat, and it is allowing the defrost cycle to stay on too long, a timer that gets stuck in defrost too long can cause this also. As far as adjusting the cut in cut out, I never touch that and can't help you on that, but I'm sure someone else on here can.
|
|
|
|
Rank: Member
Groups: Registered
Joined: 10/12/2008(UTC) Posts: 4
|
Thanks very much, abadfish66, for the reply and help. I cleaned the freezer drain line and the evaporator pan. Now both freezer and refrig temperatures seem normal except for the end of the defrost cycle. Timer seems to run OK; the problem does appear to be a defective defrost termination thermostat. So my next step is to try to find, remove, and replace it. --David
|
|
|
|
Rank: Member
Groups: Registered
Joined: 10/12/2008(UTC) Posts: 4
|
I found specs on a replacement timer (8 hr cycle with 30 minute defrost time, so mine is close to normal) and a defrost heater (cutout at 55 degrees F and cut in at ~30 degrees, so it's acting about normal, too). :confused: After reading your responses and some additional thought, I hypothesized that the refrigerator was originally designed to have a (long missing) filter between the freezer (fan channel on the back wall) and the refrigerator (where the channel exits down into the refrigerator). So I added one made of a thin sheet of filter material. The temperatures in the freezer and refrigerator now appear to be correct and much more stable most of the time (0 deg F plus-or-minus about 5 deg F and 38 deg F plus-or-minus about 2 deg F, respectively). So it's all fixed! :) Thanks for your help in figuring this out! David--GibsonRT14F3
|
|
|
|
Forum Jump
You can post new topics in this forum.
You can reply to topics in this forum.
You can delete your posts in this forum.
You can edit your posts in this forum.
You cannot create polls in this forum.
You can vote in polls in this forum.
Important Information:
The AppliancePartsPros.com uses cookies. By continuing to browse this site, you are agreeing to our use of cookies.
More Details
Close