Measure the freezer and fridg. temperatures before it shuts off. Also, if you set the control to a lower temperature, does it reach a lower temperature and run longer?
|
|
|
|
Rank: Member
Groups: Registered
Joined: 7/17/2013(UTC) Posts: 17
|
Fridge side 40 deg. when it starts running. After it shuts off 10 mins later, its at 33. Freezer at about 5 degrees. When it shuts off. about -2 degrees. Lowered the fridge and freezer temps, no change in cycle times. 10 on 10 off.
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 9/10/2007(UTC) Posts: 9,586
Was thanked: 2 time(s) in 2 post(s)
|
Are you sure you placed the fridg cold control sensing tubing in the original place? Seems like you have no basic refrigeration system problems, but a control problem.
|
|
|
|
Rank: Member
Groups: Registered
Joined: 7/17/2013(UTC) Posts: 17
|
Yes. I'm sure. My initial thought was that it had a bad thermostat, so I replaced it. Same results. I know its possible to have a new one be bad. Is there any way to test them? I still have the old one so it is easy to access and test.
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 9/10/2007(UTC) Posts: 9,586
Was thanked: 2 time(s) in 2 post(s)
|
Turn the cold control to the coldest setting, then measure the freezer temperature, should go well below zero, if not you do have refrigeration systems problems that gauges would confirm. You also could have a stuck damper door.
|
|
|
|
Rank: Member
Groups: Registered
Joined: 7/17/2013(UTC) Posts: 17
|
I will try those things. If I'm not mistaken, the damper door is manual that works off the freezer control slide. At least that is what I saw when I took it apart to install the thermostat. Not sure how it could stick?
|
|
|
|
Rank: Member
Groups: Registered
Joined: 7/17/2013(UTC) Posts: 17
|
Hey Rich,
I ran the cold control as cold as it would go. The freezer went well below zero. My digital gauge wouldn't read at that cold as it blacked out. My analog does not read below zero, but it buried the needle. If I were to gauge it according to the distance of the other marks on the gauge, I would say it was way more than -20 or better. Once the system shut off, it went to defrost. I did this 2 times and both times it went to the defrost cycle.
Thanks.
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 9/10/2007(UTC) Posts: 9,586
Was thanked: 2 time(s) in 2 post(s)
|
Only thing left is too much cold air into the fridg section. You might try a partial restriction of the airflow into the fridg.
|
|
|
|
Forum Jump
You can post new topics in this forum.
You can reply to topics in this forum.
You can delete your posts in this forum.
You can edit your posts in this forum.
You cannot create polls in this forum.
You can vote in polls in this forum.
Important Information:
The AppliancePartsPros.com uses cookies. By continuing to browse this site, you are agreeing to our use of cookies.
More Details
Close