I need to re-wire the control wire from my thermostat to my central AC unit. Taking a look in the manual, it shows the diagram which wire goes where, but on each of the three main wires it has a box. The boxes are labelled "Cooling system," "Fan relay" and "Heating system." Does that mean the wire should go through those systems before going to the transformer? I attached the wiring diagram for reference. Thermo is a White-Rodgers 1f80-51.
splumer attached the following image(s):
thermostat0037-5285_Page_3.jpg
Sponsor
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
kurt h  
#2 Posted : Friday, July 27, 2012 8:01:15 PM(UTC)
kurt h

Rank: Member

Groups: Registered
Joined: 7/14/2012(UTC)
Posts: 10

does your thermostat have a (c) terminal? If so hook one wire going out to your condensing unit to (c) terminal and the other to the (y) terminal. You should only have 2 wires going outside. Your t stat contacts close r to y in cooling
splumer  
#3 Posted : Sunday, July 29, 2012 2:53:30 PM(UTC)
splumer

Rank: Member

Groups: Registered
Joined: 6/23/2011(UTC)
Posts: 33

Originally Posted by: kurt h Go to Quoted Post
does your thermostat have a (c) terminal? If so hook one wire going out to your condensing unit to (c) terminal and the other to the (y) terminal. You should only have 2 wires going outside. Your t stat contacts close r to y in cooling


The terminals you see in the diagram are the only ones it has. Are you saying a two-lead wire should go from the C & Y terminals on the thermo to the outside unit? (Don't have a C terminal, but whatever)
whsydddy9  
#4 Posted : Saturday, August 4, 2012 6:04:51 AM(UTC)
whsydddy9

Rank: Member

Groups: Registered
Joined: 10/18/2010(UTC)
Posts: 41

Yellow wire should go to - Y
Green wire should go to - G
Red wire should go to - R
White wire should go to - W

Then there should be a jumper wire between RC (cool) & RH (heat)
whsydddy9  
#5 Posted : Saturday, August 4, 2012 6:06:51 AM(UTC)
whsydddy9

Rank: Member

Groups: Registered
Joined: 10/18/2010(UTC)
Posts: 41

the 2 wire from the Ac to the Furnace should be wired on the Y & C terminals - and PLEASE :eek: DISCONNECT THE POWER B4 WORKING!