Originally Posted by: richappy  Your problem is not a defrost problem. If the lowest temerature the freezer will go down to is zero, you might have a partial restriction in the capillary line. The freezer control is not set to the lowest temp-control setting #3. Freezer at 0 degrees. Every time I remove the panels & defrost with hair dryer, the noise is gone for two-three days, then returns.
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 9/10/2007(UTC) Posts: 9,586
Was thanked: 2 time(s) in 2 post(s)
|
Set the freezer control to the coldest setting and measure the stabilized freezer temperature.
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 9/10/2007(UTC) Posts: 9,586
Was thanked: 2 time(s) in 2 post(s)
|
Set the freezer control to the coldest setting and measure the stabilized freezer temperature.
|
|
|
|
Rank: Member
Groups: Registered
Joined: 11/29/2011(UTC) Posts: 10
|
Originally Posted by: richappy  Set the freezer control to the coldest setting and measure the stabilized freezer temperature. At the coldest setting for the freezer, -10 degrees overnight. Noise not as bad as before. Refrigerator temp to cold for my use at that setting.
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 9/10/2007(UTC) Posts: 9,586
Was thanked: 2 time(s) in 2 post(s)
|
Apparently if it is contamination in the capillary line, it's too small to affect refrigeration. You might try packing fibre insulation around the termination of the capillar line in the freezer, have seen this before but black rubbery like stuf was used.
|
|
|
|
Rank: Member
Groups: Registered
Joined: 11/29/2011(UTC) Posts: 10
|
Originally Posted by: richappy  Apparently if it is contamination in the capillary line, it's too small to affect refrigeration. You might try packing fibre insulation around the termination of the capillar line in the freezer, have seen this before but black rubbery like stuf was used. Turned freezer control to midrange, will better insulate the capillary line and replace the defrost heater/thermostat assembly. I will let you know If your assistance with the noise worked.
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 9/10/2007(UTC) Posts: 9,586
Was thanked: 2 time(s) in 2 post(s)
|
You can make a sound damper with cloth and silicone cement.
|
|
|
|
Rank: Member
Groups: Registered
Joined: 11/29/2011(UTC) Posts: 10
|
Originally Posted by: richappy  You can make a sound damper with cloth and silicone cement. Defrosted the evaporator coils, removed and cleaned evap drain line to drain pan, replaced the defrost heater and thermostat assy, installed refrigerant flow noise suppression kit #4318168 over the center transition to capillary tube, set freezer and refrigerator temp controls to #4 setting. Refrigerator temp at 40 degrees, Freezer temp at 10 degrees. PROBLEM SOLVED!!!!!! Thanks:)
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 9/10/2007(UTC) Posts: 9,586
Was thanked: 2 time(s) in 2 post(s)
|
|
|
|
|
Forum Jump
You can post new topics in this forum.
You can reply to topics in this forum.
You can delete your posts in this forum.
You can edit your posts in this forum.
You cannot create polls in this forum.
You can vote in polls in this forum.
Important Information:
The AppliancePartsPros.com uses cookies. By continuing to browse this site, you are agreeing to our use of cookies.
More Details
Close