bchristal  
#41 Posted : Thursday, November 13, 2008 10:40:17 AM(UTC)
bchristal

Rank: Member

Groups: Registered
Joined: 11/12/2008(UTC)
Posts: 27

Originally Posted by: abadfish66 Go to Quoted Post
Also did you replace the filterdryer?


No, could that be clogged? Enough for no performance?
abadfish66  
#42 Posted : Thursday, November 13, 2008 10:41:20 AM(UTC)
abadfish66

Rank: Advanced Member

Groups: Senior Expert
Joined: 5/28/2008(UTC)
Posts: 1,620

If it is restricted, chances are high it will be at the captube end that you brazed, or in the filterdryer. You really don't need to remove the evap.
abadfish66  
#43 Posted : Thursday, November 13, 2008 10:44:09 AM(UTC)
abadfish66

Rank: Advanced Member

Groups: Senior Expert
Joined: 5/28/2008(UTC)
Posts: 1,620

push in the schrader valve on the high side valve, do you get high pressure coming out. Also do you have any idea how much 134 you added, you may not have enough. if you add more and the low side pressure starts coming up, it should be good, you just need to add the proper amount.
abadfish66  
#44 Posted : Thursday, November 13, 2008 10:45:25 AM(UTC)
abadfish66

Rank: Advanced Member

Groups: Senior Expert
Joined: 5/28/2008(UTC)
Posts: 1,620

I would add it through the low side, that might be your problem. It's more dificult to add through the high side.
abadfish66  
#45 Posted : Thursday, November 13, 2008 10:50:53 AM(UTC)
abadfish66

Rank: Advanced Member

Groups: Senior Expert
Joined: 5/28/2008(UTC)
Posts: 1,620

Charge it with the can upside down if your not already
bchristal  
#46 Posted : Thursday, November 13, 2008 11:05:00 AM(UTC)
bchristal

Rank: Member

Groups: Registered
Joined: 11/12/2008(UTC)
Posts: 27

Yes, liquid freon comes out of the high side if I push the valve.
I've added an entire can of 134a (12 oz). Some has leaked out. It is supposed to hold 6.5 oz.
Where's the captube? The evaporator has 3 solder connections: to the compressor, to the condensor, and there's a small tube (hot gas).

I don't see how I could check for clogs without removing the evaporator.
abadfish66  
#47 Posted : Thursday, November 13, 2008 11:29:07 AM(UTC)
abadfish66

Rank: Advanced Member

Groups: Senior Expert
Joined: 5/28/2008(UTC)
Posts: 1,620

The cap tube is the real small diameter line that comes off the evap. Now that you added the entire can, what is your lowside pressure? Is the condender getting hot. Is the accumulator freezing?
v2k04  
#48 Posted : Thursday, November 13, 2008 11:33:36 AM(UTC)
v2k04

Rank: Advanced Member

Groups: Senior Expert
Joined: 10/9/2008(UTC)
Posts: 784

if you have added that much freon and it still pulls into a deep vacuum it is definitely restricted you need to isolate the high and low sides and with a process tube adaptor You blow nitrogen through it and depending on how long you left the system open it could be contaminated with moisture. flush the system real good with Nu_Calgon R11 Flush, Then flush both sides with nitrogen I would replace the line drier and then put it in a vacuum for at least an hour. Then recharge it
bchristal  
#49 Posted : Thursday, November 13, 2008 11:43:41 AM(UTC)
bchristal

Rank: Member

Groups: Registered
Joined: 11/12/2008(UTC)
Posts: 27

Originally Posted by: abadfish66 Go to Quoted Post
The cap tube is the real small diameter line that comes off the evap. Now that you added the entire can, what is your lowside pressure? Is the condender getting hot. Is the accumulator freezing?


Low side is -17. It was -20 before I added more freon.
The condensor is still cool.
The evaporator/accumulator is not getting cold.
bchristal  
#50 Posted : Thursday, November 13, 2008 11:49:47 AM(UTC)
bchristal

Rank: Member

Groups: Registered
Joined: 11/12/2008(UTC)
Posts: 27

Originally Posted by: v2k04 Go to Quoted Post
if you have added that much freon and it still pulls into a deep vacuum it is definitely restricted you need to isolate the high and low sides and with a process tube adaptor You blow nitrogen through it and depending on how long you left the system open it could be contaminated with moisture. flush the system real good with Nu_Calgon R11 Flush, Then flush both sides with nitrogen I would replace the line drier and then put it in a vacuum for at least an hour. Then recharge it


Sorry to ask, but how do you "isolate the high and low sides and with a process tube adaptor?"

I only have compressed air. Will that ruin the system? I'll pull a vacuum after I finish.

I didn't check the evaporater for clogs before I installed it. Are they ever clogged from the factory?