My Lennox heater starts up fine runs for about 4 to 5 mins. then the burners shut off.Everything else stays running except the burners.The front panel lights up a open rollout switch which I replaced hoping that was the problem.But that did not fix it.HELP PLEASE :)
|
|
|
|
Rank: Member
Groups: Registered
Joined: 1/19/2011(UTC) Posts: 3
|
|
|
|
|
Rank: Member
Groups: Registered
Joined: 1/27/2011(UTC) Posts: 12
|
It could be that the sensor in the heat exchanger is the problem. Some units have several heat sensors with or without a reset. When the unit shuts down, disconnect each sensor and ohm them out before they cool down - if you get a reading across all the ones you checked then the problem is elswhere - could be in the board. SteveKJR Originally Posted by: giantsfan My Lennox heater starts up fine runs for about 4 to 5 mins. then the burners shut off.Everything else stays running except the burners.The front panel lights up a open rollout switch which I replaced hoping that was the problem.But that did not fix it.HELP PLEASE :)
|
|
|
|
Rank: Member
Groups: Registered
Joined: 1/19/2011(UTC) Posts: 3
|
Well come to find out what was wrong with my unit was that the installer built a box in my attic for a filter for my unit.Why they would do something so stupid is beyond me.I had to air draw to my unit come to find out so I started checking my ducts to see if the came loose or became torn by something.Come to find out when I started looking around I found the box with the filter and took it out and relocated it to a more convient place to get to change.
|
|
|
|
Rank: Member
Groups: Registered
Joined: 1/27/2011(UTC) Posts: 12
|
So, it sounds like the high limit was doing the job - the filter caused an air flow problem by reducing airflow across the heat excahnger (that is if the filter you found was completely clogged up). As a result, the temperature in the heat exchanger exceeded the temp on the sensor and the unit shut down. Good find. Keep an eye on those filters - they can cause problems. SteveKJR Originally Posted by: giantsfan Well come to find out what was wrong with my unit was that the installer built a box in my attic for a filter for my unit.Why they would do something so stupid is beyond me.I had to air draw to my unit come to find out so I started checking my ducts to see if the came loose or became torn by something.Come to find out when I started looking around I found the box with the filter and took it out and relocated it to a more convient place to get to change.
|
|
|
|
Forum Jump
You can post new topics in this forum.
You can reply to topics in this forum.
You can delete your posts in this forum.
You can edit your posts in this forum.
You cannot create polls in this forum.
You can vote in polls in this forum.
Important Information:
The AppliancePartsPros.com uses cookies. By continuing to browse this site, you are agreeing to our use of cookies.
More Details
Close