When I put the probes of my multimeter to any two probes of the compressor am I supose to get a reading of zero ohms? I'm getting a reading of 8.8 4.9 & 4. is that normal?
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 2/29/2008(UTC) Posts: 19,638
Thanks: 1 times Was thanked: 11 time(s) in 11 post(s)
|
|
THIS FORUM IS DEAD!!!!!!! |
|
|
|
Rank: Member
Groups: Registered
Joined: 11/15/2009(UTC) Posts: 43
|
Do you have any idea why the compressor would start buzzing and then click off from time to time? I have cleaned the condenser and replaced the overload relay.
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 2/29/2008(UTC) Posts: 19,638
Thanks: 1 times Was thanked: 11 time(s) in 11 post(s)
|
Check to ensure the compressor/condenser fan is running. Is the compressor very hot when it does this? Could be the compressor is seizing, overheating and tripping out. When you replaced the relay did it come with a new capacitor (as per Item 12 in Section 6). Could be the capacitor is leaking current. |
THIS FORUM IS DEAD!!!!!!! |
|
|
|
Rank: Member
Groups: Registered
Joined: 11/15/2009(UTC) Posts: 43
|
The condenser fan is running and and the new relay did come w a new capacitor. the compressor seems to be a little warmer than usual.
|
|
|
|
Rank: Member
Groups: Registered
Joined: 11/15/2009(UTC) Posts: 43
|
the fridge will run fine if i unplug it for an hour or so then plug it back in. then it will run till its up to the proper temp and then shut off. when I turn the temp up the compressor will click on, buzz for about 10 seconds then click back off. it will keep doing this over and over. is it possible that I have a restriction inside the sealed system?
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 2/29/2008(UTC) Posts: 19,638
Thanks: 1 times Was thanked: 11 time(s) in 11 post(s)
|
[COLOR="Blue"]is it possible that I have a restriction inside the sealed system?[/COLOR] May be a possibility but if you have a plug it would be there all the time. More likely the motor is heating up and seizing. Or at least increasing it's mechanical resistance to the point where the start can get it to start. |
THIS FORUM IS DEAD!!!!!!! |
|
|
|
Rank: Member
Groups: Registered
Joined: 11/15/2009(UTC) Posts: 43
|
Could it be a floating restriction? The fridge is about 5 years old. can it develop a restriction even though the sealed system has never been entered? Should I go ahead and do a sweep charge and replace the compressor?
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 2/29/2008(UTC) Posts: 19,638
Thanks: 1 times Was thanked: 11 time(s) in 11 post(s)
|
[COLOR="Blue"]Could it be a floating restriction? The fridge is about 5 years old. can it develop a restriction even though the sealed system has never been entered?[/COLOR] Cannot say for sure but it would be unlikely as I cannot see it being this consistent. To me it makes more sense that it is a compressor problem. [COLOR="Blue"]Should I go ahead and do a sweep charge and replace the compressor?[/COLOR] I would get a quote on this as often it makes more sense to replace the unit. I would check the unit's age as it has a 5 year warranty on the sealed system. http://shared.whirlpoolcorp.com/assets/pdfs/literature/Warranty%20Page%20-%202225033-W.pdf |
THIS FORUM IS DEAD!!!!!!! |
|
|
|
Forum Jump
You can post new topics in this forum.
You can reply to topics in this forum.
You can delete your posts in this forum.
You can edit your posts in this forum.
You cannot create polls in this forum.
You can vote in polls in this forum.
Important Information:
The AppliancePartsPros.com uses cookies. By continuing to browse this site, you are agreeing to our use of cookies.
More Details
Close