#1 Posted : Wednesday, March 7, 2012 10:08:38 AM(UTC)
Quote
WI-landlord

Rank: Member

Groups: Registered
Joined: 3/7/2012(UTC)
Posts: 2

Hello,

I'm trying to repair a fridge that went out in on of my apratments.
It's a Frigidaire Model FRT18TPHWO - freezer on top model.
Neither the fridge or the freezer compartments are getting cold, so I'm looking for advice from the experts.

Here's the situation:
I suspected a problem in the defrost circuit, so I went ahead & installed a new defrost timer and new defrost thermostat. They were easy enough to just replace. I still have the back cover removed from the freezer section and want to see if the new components fixed the problem. It appears that they haven't.
The refrigerator powers up, light in fridge works, compressor is running, circulation fan in freezer compartment is running, temperature control knob is turned all the way up to "coldest", switch in fridge compartment is set to "reduce exterior mositure".
I've let it run for about a half hour and when I open the freezer and feel the coils on the evaporator, they are not getting cold. They are still at room temperature at best. Thus, the fridge and freezer are not and will not get cold.
I do not see any evidence that the compressor or refrigerant lines/evaporator/condensor could be damaged (i.e. loss of refrigerant).

What did I miss? What else could this situation be caused by?
I'll appreciate any advice on this matter.

Thanks in advance!
Ron
Sponsor
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
Joe / APP Team  
#2 Posted : Wednesday, March 7, 2012 10:47:54 AM(UTC)
Quote
Joe / APP Team

Rank: Advanced Member

Groups: Moderators
Joined: 7/14/2010(UTC)
Posts: 5,222

Was thanked: 1 time(s) in 1 post(s)
Originally Posted by: WI-landlord Go to Quoted Post
Hello,

I'm trying to repair a fridge that went out in on of my apratments.
It's a Frigidaire Model FRT18TPHWO - freezer on top model.
Neither the fridge or the freezer compartments are getting cold, so I'm looking for advice from the experts.

Here's the situation:
I suspected a problem in the defrost circuit, so I went ahead & installed a new defrost timer and new defrost thermostat. They were easy enough to just replace. I still have the back cover removed from the freezer section and want to see if the new components fixed the problem. It appears that they haven't.
The refrigerator powers up, light in fridge works, compressor is running, circulation fan in freezer compartment is running, temperature control knob is turned all the way up to "coldest", switch in fridge compartment is set to "reduce exterior mositure".
I've let it run for about a half hour and when I open the freezer and feel the coils on the evaporator, they are not getting cold. They are still at room temperature at best. Thus, the fridge and freezer are not and will not get cold.
I do not see any evidence that the compressor or refrigerant lines/evaporator/condensor could be damaged (i.e. loss of refrigerant).

What did I miss? What else could this situation be caused by?
I'll appreciate any advice on this matter.

Thanks in advance!
Ron


Ron,
If the compressor starts and runs, the whole test period time, or more than a minute or two, you'd have to have a refrigerant leak, and no refrigerant in the system.
If you have a clamp on amp meter, I'd expect an amperage draw of 2.5 to 4.5 amps, if the compressor is running and the system has the proper sized refrigerant draw.

Thanks and Good Luck,
:) :) :) :)
WI-landlord  
#3 Posted : Wednesday, March 7, 2012 6:50:15 PM(UTC)
Quote
WI-landlord

Rank: Member

Groups: Registered
Joined: 3/7/2012(UTC)
Posts: 2

Thanks for the advice Joe. I will check the current draw of the compressor as you suggest.
Joe / APP Team  
#4 Posted : Thursday, March 8, 2012 5:09:38 AM(UTC)
Quote
Joe / APP Team

Rank: Advanced Member

Groups: Moderators
Joined: 7/14/2010(UTC)
Posts: 5,222

Was thanked: 1 time(s) in 1 post(s)
Originally Posted by: WI-landlord Go to Quoted Post
Thanks for the advice Joe. I will check the current draw of the compressor as you suggest.


WI,
OK, That's quick way to test a system. Low amp draw(> 1 amp) would indicate a bad compressor or no refrigerant in the sealed sytem. You'll be able to decide which direction to go from there.

:) :) :)
Quick Reply Show Quick Reply
Users browsing this topic
New Topic Post Reply
Forum Jump  
You can post new topics in this forum.
You can reply to topics in this forum.
You can delete your posts in this forum.
You can edit your posts in this forum.
You cannot create polls in this forum.
You can vote in polls in this forum.