i checked voltage on the two lines going to starter relay. while the frig circulating? pump was on the voltage measured around 128v, when the buzzing noise started it dropped to around 124.
the voltage at the receptacle measured around 128v. this is surprising, since i thought that the voltage was supposed to be 115-120.
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 9/10/2007(UTC) Posts: 9,586
Was thanked: 2 time(s) in 2 post(s)
|
As Gene mentioned, do not use a 3 n 1 start device,will burn out a modern R134A compressor. As Gene sugested, you might have a bad control pc board, if it at times,it turns off the compressor, then tries to re-start within a short period oif time before the system pressures equalize.
|
|
|
|
Rank: Member
Groups: Registered
Joined: 8/21/2012(UTC) Posts: 14
|
it would be nice to find that problem was the control board rather than compressor. i had a repairman out who listened to the frig, tried rocking the compressor, heard that i had replaced the starter and tested resistance at the 3 compressor pins; decided that it was a failed compressor. the control board didn't come up.
how soon restarting is too soon? how long might system pressure take to equalize? would pressure not being equalized cause the compressor to not start, hence the buzzing noise?
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert, Administrators Joined: 7/19/2007(UTC) Posts: 27,455
Was thanked: 4 time(s) in 4 post(s)
|
Order the control board and install it. If it would not fix the problem then you can return it for full refund.
Gene.
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 9/10/2007(UTC) Posts: 9,586
Was thanked: 2 time(s) in 2 post(s)
|
If he failed to check current draw and system pressures, and just tested compressor winding resistance with ohmeter, he did not confirm a bad compressor. System pressures take a few minutes to equalize, if the control is trying to re-start with less time, you have a bad control board.
|
|
|
|
Forum Jump
You can post new topics in this forum.
You can reply to topics in this forum.
You can delete your posts in this forum.
You can edit your posts in this forum.
You cannot create polls in this forum.
You can vote in polls in this forum.
Important Information:
The AppliancePartsPros.com uses cookies. By continuing to browse this site, you are agreeing to our use of cookies.
More Details
Close