raptor0192  
#1 Posted : Monday, August 22, 2016 7:54:44 AM(UTC)
Quote
raptor0192

Rank: Member

Groups: Registered
Joined: 8/22/2016(UTC)
Posts: 2

Hi all,

A commercial True T-49 fridge at our church just started blowing hot air.

Pulled off the overload, and it checks out fine. Checked the compressor terminals, and I read 6 ohms on terminals R to S, 1 ohm on terminals R to C, and 5.0 ohms on terminals C to R, so they add up (but seem low?).

But when I check the start relay, it seems bad. When I check from terminals S to L, I get a short, then when I turn the relay over I get open. And when I measure S to M OR when I measure L to M, I get open all the time, even when I turn the relay over. So, bad relay, right? It is a 3ARR2 KCR181S. Can't seem to find one anywhere. Thoughts?

Thanks so much!!
Sponsor
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
Dean Haustead  
#2 Posted : Friday, August 26, 2016 4:10:54 AM(UTC)
Quote
Dean Haustead

Rank: Member

Groups: Registered
Joined: 6/13/2016(UTC)
Posts: 72

If you're on a commercial refrigerator troubleshooting call and the compressor is running with low amp draw, low suction pressure, and low discharge pressure, you may have a low charge, or a restricted liquid line, drier, or metering device. Check the superheat and subcooling, and make the necessary repairs.
raptor0192  
#3 Posted : Friday, August 26, 2016 8:13:46 AM(UTC)
Quote
raptor0192

Rank: Member

Groups: Registered
Joined: 8/22/2016(UTC)
Posts: 2

Originally Posted by: Dean Haustead Go to Quoted Post
If you're on a commercial refrigerator troubleshooting call and the compressor is running with low amp draw, low suction pressure, and low discharge pressure, you may have a low charge, or a restricted liquid line, drier, or metering device. Check the superheat and subcooling, and make the necessary repairs.


That has nothing to do with what I said...
It was the start relay and capacitor, by the way.
Dean Haustead  
#4 Posted : Wednesday, May 24, 2017 2:29:46 AM(UTC)
Quote
Dean Haustead

Rank: Member

Groups: Registered
Joined: 6/13/2016(UTC)
Posts: 72

I have no idea about your post.
Quick Reply Show Quick Reply
Users browsing this topic
New Topic Post Reply
Forum Jump  
You can post new topics in this forum.
You can reply to topics in this forum.
You can delete your posts in this forum.
You can edit your posts in this forum.
You cannot create polls in this forum.
You can vote in polls in this forum.