Kenmore 21 Model 363.9611780 Serial L11642092 On the coldest settings for both the refrigerator and freezer and the freezer registers 32 degrees and the refrigerator 50 degrees. This is after I unplugged and completely defrosted for 36 hours. Before unplugging the freezer had ice build-up on the back wall. In some places it was 3/4 inch thick. I can't afford a new refrigerator/freezer right now. I'd like to repair this one if I can. Please help.
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 10/31/2007(UTC) Posts: 214
|
This has all the indications of a failed defrost cycle... Your model number is not coming up positive for a match so unless you feel competent electrically checking out components on your model then suggest you call a pro to troubleshoot the problem....
|
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 2/29/2008(UTC) Posts: 19,638
Thanks: 1 times Was thanked: 11 time(s) in 11 post(s)
|
Your model number does not come up please check it. I can find some info on a 363-9611781 which may be close to yours if the number you listed is indeed correct.
Your original problem does sound like a defrost problem which should have been temporarily fixed when you did a manual defrost.
How long have you waited for the unit to get back down to temperature? It needs a minimum of 12 hours. Also if the unit did a defrost cycle this could slow the process down as it would shut the compressor off for half an hour or so. Is the compressor still running? If yes then it is still trying to get to set point. Recommended temperatures are 0 to 5 degrees in the freezer and about 40 degrees in the fresh food.
Is the evaporator (freezer) fan running? Is the condenser (compressor) fan running?
If it does not get down to the correct temperatures and the compressor is running, remove the evaporator cover in the freezer so you can check the coils. If there is just frost in one area (usually where the freon enters the coils) then you are probably low on freon. This would be an expensive repair.
Since this post is fairly long I will do another post to address the original problem. |
THIS FORUM IS DEAD!!!!!!! |
|
|
|
Rank: Advanced Member
Groups: Senior Expert
Joined: 2/29/2008(UTC) Posts: 19,638
Thanks: 1 times Was thanked: 11 time(s) in 11 post(s)
|
Defrost Problem Repair
OK, using the 363-11781 parts and assuming yours is the same and this may be the wrong assumption.
First remove the evaporator cover in the freezer so you can see the coils. Do not let them de-ice. If they are heavily iced/frosted over you have a defrost problem. We are a little late on the above but the defrost thermostat can be closed by holding it's face onto an ice cube. Just be very careful to not touch the connections.
If yes. Manually force a defrost cycle by turning the defrost timer cam with a screw driver till the fans and compressor turn off. Often it is under the unit at the front or the back. They are also often in the control console, in this case there is usually a hole in the cover to let you get at the timer cam Now check the defrost heater to see if it is on. Be careful you do not want to burn your fingers. If the heater is on then the timer needs replacing, re: it is probably stalling during it's rotation so is never getting into a defrost cycle.
If not on. Unplug the unit. Remove the wire for one side of the heating element from the wiring and measure it for continuity, usually around 20 ohms or so.
If the heater is OK Remove one wire to the defrost thermostat and measure it, should be 0 ohms when frozen. Note that it opens just above freezing so must be frozen to check it. Also inspect it, if it is bulged at all replace it even if it measures OK.
If both the above are OK then odds are the defrost timer contacts are toast. Best way to test this is a live test to see if you have 120 volts across the heater/defrost thermostat combo.
Here are the parts I found for the 781 unit. You can look them up at AppliancePartsPros. They all have pictures which will let you compare them to what is in your unit. Defrost Thermostat - AP2071242 Defrost Timer - AP2061693 Defrost Heater - AP2071484
If you do not own a meter, I would suggest you purchase a one. You can get a decent digital multimeter for under $20.00. You do not need fancy though it is nice if the leads are a couple feet long. If it saves ordering one unnecessary part it has paid for itself and you end up owning a useful tool. Most places will not let you return electrical parts so if you order it, you own it. A couple things to watch when measuring ohms and continuity 1. Always remove power from the machine otherwise you could blow your meter. 2. Always disconnect at least one side of any device you are checking. This eliminates the possibility of measuring an alternate/parallel circuit path. 3. When checking for closed contacts and continuity use the lowest scale (Usually 200 ohms). Then try higher scales. This scale is 0 to 200 ohms so if the device you are measuring is 300 ohms this scale would show an open circuit which it is not, you are just measuring outside the scale's dynamic range.
There is a good STICKY at the start of this forum about it's use. |
THIS FORUM IS DEAD!!!!!!! |
|
|
|
Forum Jump
You can post new topics in this forum.
You can reply to topics in this forum.
You can delete your posts in this forum.
You can edit your posts in this forum.
You cannot create polls in this forum.
You can vote in polls in this forum.
Important Information:
The AppliancePartsPros.com uses cookies. By continuing to browse this site, you are agreeing to our use of cookies.
More Details
Close