Check windings of compressor, com-start, com-run and run-start windings should all be the same ohms, if not, the compressor is bad and frying the invertor.
|
|
Compressor and condenser not coming on, 3 prong connector from inverter compressor board not getting 21 volts to any of 3 to each other but to ground getting 21 volts to any of the 3 connector contacts. How many volts to inverter compressor board should there be? New inverter compressor board and main boards were installed Thanks Ronson ggm@luckymail.com 530-545-3711 2-25-13
|