you may want to get ahold of your l.p. Provider to have them check gas pressure. Often times water will get into regulators vent and freeze.causing diaphram to open or close more than it should,... |
|
gas pressure could be your problem. But not likely.you can buy a cheap manometer to check it though. If its locking out more often when its windy id think inducer fan, vent pipe,combustion air pipe... |
|
a very common problem with the flame rod (sensor) is that over time a thin layer of carbon will build up on rod and send a false signal to the ignition module causing it to lock out.usually you can... |
|
hey slugranch.i didnt mean you were wrong.in fact in this case i think you are 100 percent right. I just recently found out about this change in 410a units using discharge filters.(i still dont think... |
|
there are many heat pump manufacturers that are using a sporlan filter drier designed for 410a and for use in the discharge line.i questioned it and called sporlan. they informed me that this is... |
|
could be plugged filter somewhere in return duct. Maybe a bad limit switch.what code flashes when in lockout? |
|
may have noncondensables in system.(moisture freezing in txv.a drop of solder stuck in txv) did you pull a deep vacuum before charging?did you change filter drier?did you put txv bulb back on line... |