Will my unit work?

 in

Heating, Ventilation, and Air Conditioning (HVAC)

. "

I have a Puron 2.5 ton condensing unit, I also have a 2 ton air handler (r-22), and

..."
 
 
Register | FAQ's | New Posts | Today's Posts | Extras
Appliance Repair Forum > Appliance Repair Help > Heating, Ventilation, and Air Conditioning (HVAC) » Will my unit work?

Post New Thread  Reply By reading any content on this site you agree to AppliancePartsPros.com, Inc. disclaimer and Terms of Use.
 
LinkBack Thread Tools Search this Thread Display Modes
  #1 (permalink)  
Old 05-07-2008, 10:01 AM
Suburbob Suburbob is offline
Junior Member
 
Join Date: May 2008
Posts: 1
Suburbob is on a distinguished road
Default Will my unit work?
Brand: -brand-   Age: Less than 1 year   

Appliance Parts from AppliancePartPros.com
I have a Puron 2.5 ton condensing unit, I also have a 2 ton air handler (r-22), and I have a txv kit to switch the handler to Puron. Will this unit work at all in a small 800 sq. ft. cabin. I know it not designed as such but I already own these pieces and would like to use them. thank you.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
  #2 (permalink)  
Old 05-08-2008, 02:05 PM
SublimeMasterJW SublimeMasterJW is offline
Senior Expert
APP Volunteer
 
Join Date: May 2008
Location: Mobile,Al
Posts: 636
SublimeMasterJW is on a distinguished road
Default You might have to tweak it a little but oh yeah.

I think it will work fine for a cabin.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #3 (permalink)  
Old 10-26-2008, 08:04 AM
Colester Colester is offline
Junior Member
 
Join Date: Oct 2008
Posts: 3
Colester is on a distinguished road
Default

The prior rely - "oh yeah" will lead you into trouble.
1st, if the R-22 is not correctly removed Completely from the system the new compressor with Puron (R-410A) will have a greatly reduced life expectancy.
2nd, matching a 2-1/2 ton condenser to a smaller 2 ton evaporator is not recommended - may work, but charging & efficiency is off the the charts.
3rd, WHY do you need a 2 or a 2-1/2 ton anything for 800 square feet? All I can assume is the is NO insulation, or it is all glass.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #4 (permalink)  
Old 10-26-2008, 04:30 PM
icehouse icehouse is offline
Senior Expert
APP Volunteer
 
Join Date: Sep 2008
Location: Bay Shore, NY
Posts: 363
icehouse is on a distinguished road
Default

Fact:
Puron
should not be used in R 22 systems at all as it is highly
miscible
and no matter how hard you try, you will not
remove
the moisture left behind.
__________________
NATE, HVAC Ecellence, NCCER, PHCC Certified Instructor. Vist www.hvacbob.com
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #5 (permalink)  
Old 10-26-2008, 06:46 PM
Colester Colester is offline
Junior Member
 
Join Date: Oct 2008
Posts: 3
Colester is on a distinguished road
Default

Suburbob should be thouroughly confused now that (2) Senior Experts/APP Volunteers have given conflicting advice.
Hello icehouse
There is a product produced by Nu-Calgon called Rx-11 Flush. this is one of the products produced with is spoke of in the following helpful article.

Tech Tip: Flushing Refrigerant Lines For Use with R-410A
07/15/2008
by Kevin O’Neill
When you replace an air conditioner or heat pump and upgrade from R-22 to R-410A, the ideal solution is to replace your refrigerant lines. This is because the mineral oil used in R-22 systems is not compatible with the new R-410A refrigerant and oil. (Note that about 3 to 5% of the compressor oil is circulated through the system, with the rest remaining in the compressor.
count = 'square300' + ++square300count;randomness = Math.random() * 100000;document.write('')R-22 is a hydrochlorofluorocarbon (HCFC) with an affinity for mineral oil, because of the chlorine atoms in the refrigerant molecule. R-410A is a hydrofluorocarbon (HFC) and it has no affinity for the mineral oil. There’s no chlorine in it, so the mineral oil in the system (refrigerant lines) that’s left over from the old system tends to hang up in the refrigerant lines and the new indoor coil. This reduces efficiency by reducing heat transfer in the coil. It can also cause unwanted chemical reactions with the new refrigerant.
R-410A uses synthetic oil called polyolester (POE), which is chemically derived from an alcohol. Moisture left in the system with the old oil breaks the new oil down and it changes back to an alcohol, ruining its lubrication properties, causing the new compressor to fail.
Customers would go through a real hardship to replace refrigerant lines, so some companies have developed flushing agents to remove the old oil and other contaminants from the refrigerant lines. Technicians can flush the lines by cutting the indoor coil loose, and then soldering the lines together indoors. Next, we inject the flushing agent into the liquid line port outside, with a hose connected to the vapor line port outside. The hose connected to the liquid line port outside discharges into a bucket or other container. We follow the flushing agent with nitrogen under pressure to make sure the flushing agent and contaminants are forced out of the system into the bucket. After the flush, we pull a vacuum on the system with a vacuum pump to evaporate any flushing agent left as well as to remove the nitrogen and any remaining air or moisture.
Flushing lines may not be absolutely necessary in all cases, but it’s inexpensive insurance against problems, similar to installing a new liquid line drier every time you open the refrigeration system.
Kevin O’Neill, CM, is the co-owner of O’Neill-Bagwell Cooling & Heating, Myrtle Beach, SC. He has 31 years experience in the HVAC service business, is a 24-year member of RSES, and was a finalist in the 2005 NATE Certified Technician Competition. Kevin can be reached at 843/385-2220; email koneill@ sc.rr.com.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #6 (permalink)  
Old 10-26-2008, 07:15 PM
icehouse icehouse is offline
Senior Expert
APP Volunteer
 
Join Date: Sep 2008
Location: Bay Shore, NY
Posts: 363
icehouse is on a distinguished road
Default

The unsaturated hydrocarbons and the sulphur compounds contained in mineral oils may react with the refrigerant. Due to this chemical reaction the oil gradually becomes darker until, eventually, it turns black.
The reaction products, which are insoluble in the oil, remain in the compressor or the refrigeration system (mainly in the evaporator and the condenser) as residues or sludge.
These residues may bring down refrigeration or air conditioning efficiency (due to reduced heat transfer in the heat exchangers) and noticeably affect operational reliability.
Experience shows that blackening and acidification of the oil can be accelerated in particular by the presence of air and water in the refrigeration cycle (up to 3% of water is possible).
In addition to that, abrasive wear caused by oil sludge may directly attack various compressor components.
This is from a leading manufacturer of lubricants.It is why replacement of lines is recommended.
We have tried the RX-11 and have still seen problems.
__________________
NATE, HVAC Ecellence, NCCER, PHCC Certified Instructor. Vist www.hvacbob.com
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #7 (permalink)  
Old 10-26-2008, 11:28 PM
miken miken is offline
Junior Member
 
Join Date: Jan 2008
Posts: 2
miken is on a distinguished road
Default Air Conditioning Repair if you ask We Will Help

The recommended pressures for the r-22 coil are lower than for 410-a (puron) so you will be more prone to a leak failure but I can tell you for sure that it will work because I have done it (shh! don't tell the manufacturers). Obviously it is recommended to replace both pieces of equipment but yes it will work just make sure your expansion valve matches your condensor and make sure your subcooling is right (10-14 degrees) and the most important thing is to make sure you are not flooding back refrigerant, this should not be a problem if the subcooling is right but it needs to be checked and it will depend on your return air temp. you should have a chart in the installation instructions of the condensor. Of course all this advice does you no good unless you have guages thermometers and an EPA certification.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #8 (permalink)  
Old 10-27-2008, 08:05 AM
icehouse icehouse is offline
Senior Expert
APP Volunteer
 
Join Date: Sep 2008
Location: Bay Shore, NY
Posts: 363
icehouse is on a distinguished road
Default

From J.Andrew Schoen of Sporlan Valves: Due to the fact that R-410A reaches critical temperature at 160°F, while R-22 reaches critical temperature at 205°F. you will have to increase the size of the unit.Especially in high ambient territories.
__________________
NATE, HVAC Ecellence, NCCER, PHCC Certified Instructor. Vist www.hvacbob.com
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
Reply



Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Evaporator unit frozen jgomez1528 Refrigerator & Freezer Repair 1 03-19-2008 11:20 AM
3-in-1 Unit Repair Proposal scott123 Oven Repair (including Ranges and Cooktops) 2 10-18-2007 05:25 AM
Unit tripping breaker tadtv Refrigerator & Freezer Repair 0 08-13-2007 06:05 PM
ac window unit trae southard Heating, Ventilation, and Air Conditioning (HVAC) 0 08-10-2007 02:33 PM
Only 1 fan speed / Unit turns itself off KenK Heating, Ventilation, and Air Conditioning (HVAC) 0 08-09-2007 09:25 AM



All times are GMT -7. The time now is 03:46 PM.

The content on this web site is for informational purposes only and is not intended to replace an on-site diagnosis from a qualified appliance service technician. By reading any content on this site you agree to AppliancePartsPros.com , Inc. disclaimer and Terms of Use.
Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
LinkBacks Enabled by vBSEO 3.0.0

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16