Gas Furnace Fan Occasionally Keeps Running After Cooldown

 in

Heating, Ventilation, and Air Conditioning (HVAC)

. "

Please bear with me as I know little if anything about heaters but am patient when it comes to sorting

..."
 
 
Register | FAQ's | New Posts | Today's Posts | Extras
Appliance Repair Forum > Appliance Repair Help > Heating, Ventilation, and Air Conditioning (HVAC) » Gas Furnace Fan Occasionally Keeps Running After Cooldown

Post New Thread  Reply By reading any content on this site you agree to AppliancePartsPros.com, Inc. disclaimer and Terms of Use.
 
LinkBack Thread Tools Search this Thread Display Modes
  #1 (permalink)  
Old 01-30-2010, 11:53 AM
Junior Member
 
Join Date: Jan 2010
Posts: 14
Dr_Zoidberg57 is on a distinguished road
Exclamation Gas Furnace Fan Occasionally Keeps Running After Cooldown
Model Number: 396GAW000075   Brand: -other-   Age: More than 10 years   

Appliance Parts from AppliancePartPros.com
Please bear with me as I know little if anything about heaters but am patient when it comes to sorting through a home repair problem, handy with tools and can follow directions.

I have a 25 year old central forced air gas furnace. According to the label inside, it is a Carrier model number 396GAW000075. I first noticed that occasionally after the fan would shut down, following its cool down cycle, about 30 seconds later it would come back on for about a minute and then turn off. Then I discovered, over the last two nights, right after the set-back time on the thermostat, if the heater happened to be on, the fan would continue to run long after the burners shut down. I checked the thermostat and confirmed that the fan was set to "automatic". I feared that I would have to unplug the furnace as the only means to shut off the fan. As a last resort, I over-rode the temperature set on the thermostat and got the burners to light again. This time the fan shut off following the cool down cycle. As yet, I have not noticed the continuous running happen at any other time.

In searching this and other sites for a diagnosis of my situation, it seems that I may have a failing fan limit control switch. If that is the case, none of the answers I looked at described where it would be located on the furnace or what it looks like.

Any assistance would be greatly appreciated.

Gerry

Ads By Google

Related Models
Whirlpool 3C 
Whirlpool 3CA2000XMW0 
Whirlpool 3CA2100XMW0 
Whirlpool 3CA2100XMW1 
Whirlpool 3CA2781XSW0 
Whirlpool 3CA2781XSW1 
Whirlpool 3CAP2762BN0 
Whirlpool 3CAP2762BW0 
Whirlpool 3CAP2782BN0 
Whirlpool 3CAP2782BW0 
Whirlpool 3CDA1100W1 
Whirlpool 3CDA1100W2 
Whirlpool 3CDA1100W5 
Whirlpool 3CDA2000F1 
Whirlpool 3CDA2000G0 
Whirlpool 3CDA2000W0 
Whirlpool 3CDE1700W0 
Whirlpool 3CE2110XMW0 
Whirlpool 3CE2110XMW1 
Whirlpool 3CE2110XMW2 
Whirlpool 3CE2910XSN0 
Whirlpool 3CE2910XSN1 
Whirlpool 3CE2910XSW0 
Whirlpool 3CE2910XSW1 
Whirlpool 3CEP2910BW0 
Whirlpool 3CEP2910DW0 
Whirlpool 3CEP2920DW0 
Whirlpool 3CEP2950DN0 
Whirlpool 3CEP2950DW0 
Whirlpool 3CEP2960DN0 
Whirlpool 3CEP2960DN2 
Whirlpool 3CEP2960DW0 
Whirlpool 3CEP2960DW2 
Whirlpool 3CFA2000W1 
Whirlpool 3CFA2000W3 
Whirlpool 3CFA2000W4 
Whirlpool 3CFA2000W5 
Whirlpool 3CFA2000W6 
Whirlpool 3CFCH4AE93 
Whirlpool 3CFCH4AS93 
Whirlpool 3CFCH4WE93 
Whirlpool 3CFCH4WS93 
Whirlpool 3CFCHWE93 
Whirlpool 3CFCS3AE92 
Whirlpool 3CFCS3AS92 
Whirlpool 3CFCS3WE92 
Whirlpool 3CFCS3WS92 
Whirlpool 3CFE2500W0 
Whirlpool 3CFE2500W2 
Whirlpool 3CFE2510W1 
Whirlpool 3CFE2510W2 
Whirlpool 3CG2901XSN0 
Whirlpool 3CG2901XSN1 
Whirlpool 3CG2901XSN3 
Whirlpool 3CG2901XSW0 
Whirlpool 3CG2901XSW1 
Whirlpool 3CG2901XSW3 
Whirlpool 3CGP2901DN0 
Whirlpool 3CGP2901DW0 
Whirlpool 3CGP2901DW1 
Whirlpool 3CGP2951BN0 
Whirlpool 3CGP2951BW0 
Whirlpool 3CGP2951DN0 
Whirlpool 3CGP2951DW0 
Whirlpool 3CGP2951DW1 
Whirlpool 3CSE3A1 
Whirlpool 3CSE3W1 
Whirlpool 3CSE5A2 
Whirlpool 3CSE5W2 
Whirlpool 3CSP2760BN0 
Whirlpool 3CSP2760BW0 
Whirlpool 3CSP2761BN0 
Whirlpool 3CSP2761BW0 
Whirlpool 3CSP2761BW1 
Whirlpool 3CSS3A1 
Whirlpool 3CSS3W1 
Whirlpool 3CSS5A2 
Whirlpool 3CSS5W2 
Whirlpool 3CTBE4A 
Whirlpool 3CTUE4A 
Whirlpool 3DWED5605SQ0 29" Electric Dryer
Whirlpool 3EAC50 
Whirlpool 3EAD19SKWR0 
Whirlpool 3EAD19XMWR0 
Whirlpool 3EAD19XMWR1 
Whirlpool 3ECKMF10 
Whirlpool 3ECKMF11 
Whirlpool 3ECKMF86 
Whirlpool 3ECKMF87 
Whirlpool 3ECKMF9 
Whirlpool 3ED22DQXAN00 
Whirlpool 3ED22DQXAW00 
Whirlpool 3ED22DQXBN00 
Whirlpool 3ED22DQXBN02 
Whirlpool 3ED22DQXBN03 
Whirlpool 3ED22DQXBW00 
Whirlpool 3ED22DQXBW02 
Whirlpool 3ED22DQXBW03 
Whirlpool 3ED22DQXDN00 
Whirlpool 3ED22DQXDN03 
Whirlpool 3ED22DQXDW00 
Whirlpool 3ED22DQXDW03 
Whirlpool 3ED22DWXTN00 
Whirlpool 3ED22DWXTN01 
Whirlpool 3ED22DWXTW00 
Whirlpool 3ED22DWXTW01 
Whirlpool 3ED22RQXXW00 
Whirlpool 3ED25DQXAN00 
Whirlpool 3ED25DQXAW00 
Whirlpool 3ED25DQXBN00 
Whirlpool 3ED25DQXBN01 
Whirlpool 3ED25DQXBW00 
Whirlpool 3ED25DQXBW01 
Whirlpool 3ED25DQXDN00 
Whirlpool 3ED25DQXDW00 
Whirlpool 3ED25DQXVN00 
Whirlpool 3ED25DQXVN01 
Whirlpool 3ED25DQXVW00 
Whirlpool 3ED25DQXVW01 
Whirlpool 3ED25RQXXW00 

Last edited by Dr_Zoidberg57 : 01-30-2010 at 12:16 PM.
Reply With Quote
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
  #2 (permalink)  
Old 01-30-2010, 03:31 PM
Member
 
Join Date: Jan 2010
Posts: 59
John @ Fischers is on a distinguished road
Default

Most older gas furnaces that have standing pilot systems use a thermostat switch located in the hot air plenum that detects when the furnace is hot and turns on the blower.

These thermostats (more commonly called the Fan/Limit control) are usually made by Honeywell or white-Rogers. The typical settings for the stops are 70 to 90 "Off", 130 to 150 "On", and the "Limit" to the bottom of the slot (lowest setting) as long as you don't get nuisance shutting off of the fire. As you might guess they also control the gas valve if the furnace gets too hot.

If you have problems with the blower not shutting off, its probably sticking. There made up of bi-metal strips that eventually wear out. They come in different sizes in length. Various from 5", 8", and 11" long. Need to pull your old one out to see what size it is. Here is a picture of your control






Here is a link for your parts, but shop around. I have seen them alot cheaper than this:

5" Fan & Limit Time Delay Switch (6 wire hook up)(Honeywell): American HVAC Parts

Last edited by John @ Fischers : 01-30-2010 at 03:39 PM.
Reply With Quote
  #3 (permalink)  
Old 01-30-2010, 04:01 PM
Junior Member
 
Join Date: Jan 2010
Posts: 14
Dr_Zoidberg57 is on a distinguished road
Default

Thank you for your assistance. I believe my furnace has electronic ignition. I did manage to remove the schematic from the upper cover of the furnace and scan it. Hopefully it will be legible enough and will enable those with vastly more knowledge than I have to figure out what I need to do.
Attached Images
File Type: jpg Actual Heater Schematic 800 X 600.jpg (62.5 KB, 46 views)
File Type: jpg Furnace Lower Section 800 X 600.JPG (426.1 KB, 45 views)
File Type: jpg Furnace Upper Section 800 X 600.JPG (374.5 KB, 44 views)

Last edited by Dr_Zoidberg57 : 01-30-2010 at 11:35 PM. Reason: Apparently not all images uploaded properly
Reply With Quote
  #4 (permalink)  
Old 01-31-2010, 08:37 AM
Member
 
Join Date: Jan 2010
Posts: 59
John @ Fischers is on a distinguished road
Default

ok, that helps. Your blower is actually controlled from the circuit board with a glass relay. Alot of the older ones, u can actually unplug the glass relay from the circuit board.

Turn off the 120v breaker to the furnace and remove the metal cover over the control board and you should see the relay. If it's glass (you can see through it), should be able to unplug it from the board and just replace it.

If it's small and black however, you will have to replace the entire control board, since this type will not unplug from the board.

Maybe remove cover and take a pic of that. Hopefully you have a glass relay since this is somewhat cheaper route than replacing the entire board.
Reply With Quote
  #5 (permalink)  
Old 01-31-2010, 01:32 PM
Junior Member
 
Join Date: Jan 2010
Posts: 14
Dr_Zoidberg57 is on a distinguished road
Default

John;

First, thank you for your time and help. Attached are the photos you requested and if I am interpreting what I see correctly, there is indeed the relay which you described. If that is indeed the case, could you steer me in the direction of where to get a replacement?
Attached Images
File Type: jpg Heater Circuit Board 1 600 X 800.jpg (59.6 KB, 43 views)
File Type: jpg Heater Circuit Board 2 600 X 800.jpg (58.9 KB, 40 views)
Reply With Quote
  #6 (permalink)  
Old 02-01-2010, 06:31 PM
Member
 
Join Date: Jan 2010
Posts: 59
John @ Fischers is on a distinguished road
Default

I thought that looked like a Bryant control board before you took the cover off..lol.. good pics. That relay will not unplug, so you will have to replace the board.

I found a exact replacement board, well sorta of. Its the replacement board as close as you are going to get.

Only biggest difference i can see right off, is the extra terminals for the A/C, which on the current one you have now, there is none.

So you can actually hook this one up the same way the one you have now is.

RED= 24V...WHITE= Heat...Green= Fan for A/C or Manual Setting @ thermostat.(which is HIGH speed),Bigger Black wire on control board going to blower motor.

Bigger Red wire you have now on control board, is LOW speed, which is for heat.

2 wires going to transformer which is LINE Voltage(120V) to power transformer. Other 2 wires leaving transformer is the LOAD side, which is 24V going back to your control board.

Not too hard really. Think of it like this: The control board is a Motel that holds all the switching and working of the system.

The control board first has to have 120V supplied to it. Then from there, the control board supplies 120V to Transformer, which then the transformer makes 24V, and plugs back into control board to work all your 24V controls.

Your thermostat is fed with 24V from the red terminal on the control board. The 24V @ your stat, is just sitting there, waiting for YOU to tell it what to do. For example,

You click stat to Heat, and then the 24V is moved from the red wire, to the White wire on your stat, which is sent back to the control board. Once the (W) terminal (which happens to have a white wire) is energized on the control board with 24V, it starts the heating cycle. As long as (W) Terminal is energized, the heating cycle will stay on, or call for heat.

It then sends 24V through all your limits, and if there "closed" as they should be, it completes the circuit and the relay for the spark ignition will Begin sparking, and pilot light will light, or hot surface ignition will glow, depending on your application.

Once it lights, then the thermocouple(or flame sensor if hot surface) will let the gas valve open and ignite the burners. in 120 seconds(rule of thumb), the control board will energize the blower relay(close), and give 120V to the RED wire and the fan will begin running.

Once (W) terminal is de-energized due to you turning off the stat, or the stat satisfying due to temp setting, the gas valve will close, and the relay will continue to be closed and let the fan run about 180 seconds(rule of thumb), then open the 120V it was supping to the red wire, thus stopping the blower..... In a nutshell.

Knowing this, you should be ok to change out the control board. Here is a link from carrier itself i found.

Furnace Control Circuit Board Replaces two Clear Relays.(BDP, Bryant, Carrier, Payne): American HVAC Parts

Let me know what you think, or what else i can do to help ya.


Also, do me a favor. Bryant, Carrier were notorious for having cracked chambers. So before you spend money, remove the cover over the 3 burners, and get a mirror and a flashlight and look up into each chamber,(which you have 3), and make sure you see no cracks, or gashes in them. here is a couple of examples:




Last edited by John @ Fischers : 02-01-2010 at 06:42 PM.
Reply With Quote
  #7 (permalink)  
Old 02-01-2010, 07:23 PM
Junior Member
 
Join Date: Jan 2010
Posts: 14
Dr_Zoidberg57 is on a distinguished road
Default

John;

You've been a big help and again thank you so much, especially for the very detailed explanation. I learned a very long time ago that the only stupid question is the one you don't ask for fear of sounding stupid. That said, I do have a couple of question regarding the information you've provided. First, do I need to verify the part number on my circuit board to make sure that the new one is indeed the correct replacement. If so, where would the number be located? Second, I think your idea of checking the chambers for cracks is spot on. I am a bit uncertain as to where the chamber cover is located and depending on where it is, how to remove it for inspection. Is the cover what I see right behind the control valve in the photo of the lower section? If so, then removal looks pretty straight forward. I should also probably invest in an appropriate sized inspection mirror so as to be thorough because I get the feeling that, sould I find any cracks, I'm pretty much "hosed".

Again, I appreciate your patience in dealing with my lack of expertise and once I know what to do here I will get back to you ASAP with the results.

Gerry
Reply With Quote
  #8 (permalink)  
Old 02-01-2010, 07:41 PM
Junior Member
 
Join Date: Jan 2010
Posts: 14
Dr_Zoidberg57 is on a distinguished road
Default

John;

I did a quick search for the circuit board you found and, unless I'm mistaken, I found the identical board on a certain auction site for considerably less money. As I tried numerous times to post the link to the page or mention the site by name, without success, here is the item number. When you enter it in the search box of this auction site, it should take you right to the correct page. the item number is 180459964151 . It is described as Carrier Bryant Payne HH84AA020 New Upgraded Circuit Control Board.


Now to hope that I find no cracks and I might get out of this relatively unscathed and have the old "girl" make it through the remainder of winter.

Gerry

Last edited by Dr_Zoidberg57 : 02-01-2010 at 08:13 PM. Reason: Link did not post correctly
Reply With Quote
  #9 (permalink)  
Old 02-01-2010, 08:20 PM
Member
 
Join Date: Jan 2010
Posts: 59
John @ Fischers is on a distinguished road
Default

Yes, that circuit board will work. When they first made them, they only had single relay control boards, which you have now.

Wasn't too much longer after that, A/C became more popular, they added another for the A/C.

Unfortunately you probably wont find the exact board as you have now. The Link i listed will defiantly work for your application.

Quote:
I am a bit uncertain as to where the chamber cover is located and depending on where it is, how to remove it for inspection. Is the cover what I see right behind the control valve in the photo of the lower section


Yes, either 2 Phillip head screws, or 1/4, or 5/16 nut driver. Remove 2 screws and remove burner cover and look up in chambers where burners are laying in bottom of. Look around and you will see the welds, and keep looking around and make sure you don't have any cracks. Imagine the chambers as 4 inch wide walls, going from where the burners are to the top where they got to your flu box.(where the vent pipe hooks up).

As i think about it, since that furnace is as old as it is, it probably has cast iron chambers, and they take forever to crack. But just check in case.

But the board will work, and once you get it and need help, take a pic and ill give you a wiring diagram for your application.

Reply With Quote
  #10 (permalink)  
Old 02-01-2010, 08:30 PM
Junior Member
 
Join Date: Jan 2010
Posts: 14
Dr_Zoidberg57 is on a distinguished road
Default

Rather than worry about what I might find tomorrow when I do the inspection, I'll settle for being content that the bargain I found will work.

Thank you once again for all your help.

Gerry
Reply With Quote
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Question on waasher not spinning occasionally abshannon Washer Repair 3 08-06-2009 10:50 AM
Dryer stops in middle of cooldown cycle alan93 Dryer Repair 2 01-19-2009 06:01 AM
washer stops and hums, after cooldown starts again gmboetr Washer Repair 1 05-15-2008 06:42 PM
Dryer shuts down just before cooldown mrmeld Dryer Repair 3 01-21-2008 02:56 AM



All times are GMT -7. The time now is 06:46 AM.

The content on this web site is for informational purposes only and is not intended to replace an on-site diagnosis from a qualified appliance service technician. By reading any content on this site you agree to AppliancePartsPros.com , Inc. disclaimer and Terms of Use.
Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2013, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO ©2011, Crawlability, Inc.

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17