I have a Heil combination hvac unit, gas heat/ac. Mod#npgaa60e1k6.It just passed the 10 year warranty.The furnace will not ignite.

..."
 
 
Register | FAQ's | New Posts | Today's Posts | Extras
Appliance Repair Forum > Appliance Repair Help > Heating, Ventilation, and Air Conditioning (HVAC) » furnace no heat

Post New Thread  Reply By reading any content on this site you agree to AppliancePartsPros.com, Inc. disclaimer and Terms of Use.
 
LinkBack Thread Tools Search this Thread Display Modes
  #1 (permalink)  
Old 01-14-2010, 07:34 AM
Junior Member
 
Join Date: Oct 2009
Posts: 16
rleescott is on a distinguished road
Default furnace no heat
Brand: -brand-   Age: More than 10 years   

Appliance Parts from AppliancePartPros.com


I have a Heil combination hvac unit, gas heat/ac. Mod#npgaa60e1k6.It just passed the 10 year warranty.The furnace will not ignite. When the thermostat comes on, the exhaust? motor runs and continues to run but there is no ignition at the pilot, so no heat. The blower runs if fan is set to on, but, of course, not if set to auto, since the furnace doesn't fire up. I have no experience with ignitor pilots, only old style thermocouples. How do I proceed?

Reply With Quote
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
  #2 (permalink)  
Old 01-19-2010, 07:15 AM
Senior Expert
APP Volunteer
 
Join Date: May 2008
Location: Mobile,Al
Posts: 724
SublimeMasterJW is on a distinguished road
Default this video shows sequence of operation

The furnace first clears out any fumes or lingering gases by starting a draft fan motor, a timing sequence begins, after a minute and ahalf the control senses the draft through the pressure hose to the proving switch and turns on the ignitor After 30 seconds the gas valve solenoid is powered up and raw gas comes out to the glowing ignitor. At this point the control does not know if the gas was ignited and gas gas is spewing out the valve. So the control has to rely on a flame sensor/electronic thermocouple to send back confirmation. If it does not get the confimation it shuts down. If the confirmation is good then the control starts a stimer and after aminute or so the fan comes on and throws warm air into the home. So what can go wrong?
No power to control
control fuse blown
tripped safety switch
faulty ignitor
faulty sensor
faulty control board
Here is a video I found on you tube that features howit works:

FoggyFacts: HVAC trouble shooting


FoggyFacts: Furnace Auto-ignition Furnace: Quick cycling
Reply With Quote
  #3 (permalink)  
Old 01-19-2010, 02:44 PM
Junior Member
 
Join Date: Oct 2009
Posts: 16
rleescott is on a distinguished road
Default

This is a 10 year old gas elec combo unit, Heil. The rollout switch tripped. This makes me worry that the heat exchanger has a crack. Is there a video that shows burners with a mild crack. I can't tell how much dancing is too much dancing for the flame. Any techniques for proving a crack? It is the torpedo style jet burner, not ribbon style.
Reply With Quote
  #4 (permalink)  
Old 01-19-2010, 03:48 PM
Senior Expert
APP Volunteer
 
Join Date: May 2008
Location: Mobile,Al
Posts: 724
SublimeMasterJW is on a distinguished road
Default

If you think their is a leak in the heat exchanger you could get the gas company to check that. The equipment used is costly to the DIYer. I found an interesting page on this :

Guide to Furnace Heat Exchanger Inspection, Testing, Leaks - Hot Air Heat Troubleshooting & Repair Guide
Reply With Quote
  #5 (permalink)  
Old 01-24-2010, 09:25 AM
Junior Member
 
Join Date: Oct 2009
Posts: 16
rleescott is on a distinguished road
Default

I now have followup that I think will prove interesting. I reset the rollout switch and turned the unit on. Within a few minutes of constant observation of the burner pattern I observed no rollout of flames and I periodically touched the sensor surface. It was certainly warm, but not 300F, and it tripped! That suggested to me that it tripped without reaching the critical temp. I got a new 300F switch and the unit has worked ever since without shutting off.
Doesn't this mean that, although uncommon, the switch failed and caused all of this trouble? If the new switch hasn't tripped, doesn't this mean that I have no more reason to question the heat exchanger that anyone else whose heating is working without a shutdown? I am interested in your thoughts about this scenario and await your reply. If I have missed the mark, please let me know. Other thoughts also welcome.
Reply With Quote
  #6 (permalink)  
Old 01-24-2010, 10:10 AM
Senior Expert
APP Volunteer
 
Join Date: May 2008
Location: Mobile,Al
Posts: 724
SublimeMasterJW is on a distinguished road
Default

Yeah those rollout are constantly in the heat of the battle so to speak. So after a while they get weak and in need of replacement. Luckily they are not that expensive, you should keep a couple of spares on hand. Glad you could git er done
Reply With Quote
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Noisy Furnace Fan alltaken Heating, Ventilation, and Air Conditioning (HVAC) 10 05-19-2014 10:57 PM
Furnace Issues ssyba Heating, Ventilation, and Air Conditioning (HVAC) 7 05-14-2010 11:27 AM
Amana Gas Furnace Ouiserm Heating, Ventilation, and Air Conditioning (HVAC) 2 11-29-2009 09:51 AM
furnace roel Heating, Ventilation, and Air Conditioning (HVAC) 1 10-05-2009 08:28 PM
furnace no heat amati5 Heating, Ventilation, and Air Conditioning (HVAC) 0 11-28-2007 01:46 PM



All times are GMT -7. The time now is 06:43 PM.

The content on this web site is for informational purposes only and is not intended to replace an on-site diagnosis from a qualified appliance service technician. By reading any content on this site you agree to AppliancePartsPros.com , Inc. disclaimer and Terms of Use.
Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO ©2011, Crawlability, Inc.

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17