This furnace is about 35 years old, original equipment, it came with the house. The thermostat is a lot more

..."
 
 
Register | FAQ's | New Posts | Today's Posts | Extras
Appliance Repair Forum > Appliance Repair Help > Heating, Ventilation, and Air Conditioning (HVAC) » Hot air furnace problem.

Post New Thread  Reply By reading any content on this site you agree to AppliancePartsPros.com, Inc. disclaimer and Terms of Use.
 
LinkBack Thread Tools Search this Thread Display Modes
  #1 (permalink)  
Old 03-06-2008, 08:55 AM
Junior Member
 
Join Date: Mar 2008
Posts: 8
RegB is on a distinguished road
Default Hot air furnace problem.
Model Number: GH-120DE   Brand: Amana   Age: More than 10 years   

Appliance Parts from AppliancePartPros.com


This furnace is about 35 years old, original equipment, it came with the house.

The thermostat is a lot more recent, the gas valve thermocouple was replaced a couple of years ago.


SYMPTOMS:
The thermostat calls for heat, the main burner comes on, after a while the fan starts up, but after a few seconds it all shuts down and tries again in about half a minute. I have verified that the fan does actually spin.

IDEAS so far:
The gas valve, thermocouple, fan and main burner are probably OK.
I think there is "something" that is not acknowledging that the fan is spinning and pushing air. This might be an air flow sensor or a thermostatic switch, I can imagine designs that would use either.


Related Models
Admiral GH0725NXEW FREEZER- CHEST
Admiral GH1026NXEW FREEZER- CHEST
Admiral GH1526NXEW FREEZER- CHEST
Admiral GH2226NXEW FREEZER- VERTICAL
Whirlpool GH4155XPB0 MICROWAVE HOOD COMBINATION
Whirlpool GH4155XPB1 MICROWAVE HOOD COMBINATION
Whirlpool GH4155XPB2 MICROWAVE HOOD COMBINATION
Whirlpool GH4155XPB3 MICROWAVE HOOD COMBINATION
Whirlpool GH4155XPQ0 MICROWAVE HOOD COMBINATION
Whirlpool GH4155XPQ1 MICROWAVE HOOD COMBINATION
Whirlpool GH4155XPQ2 MICROWAVE HOOD COMBINATION
Whirlpool GH4155XPQ3 MICROWAVE HOOD COMBINATION
Whirlpool GH4155XPS0 MICROWAVE HOOD COMBINATION
Whirlpool GH4155XPS1 MICROWAVE HOOD COMBINATION
Whirlpool GH4155XPS2 MICROWAVE HOOD COMBINATION
Whirlpool GH4155XPS3 MICROWAVE HOOD COMBINATION
Whirlpool GH4155XPT0 MICROWAVE HOOD COMBINATION
Whirlpool GH4155XPT1 MICROWAVE HOOD COMBINATION
Whirlpool GH4155XPT2 MICROWAVE HOOD COMBINATION
Whirlpool GH4155XPT3 MICROWAVE HOOD COMBINATION
Whirlpool GH4184XSB0 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH4184XSB1 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH4184XSS0 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH4184XSS1 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5176XPB0 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5176XPB1 MICROWAVE HOOD COMBO
Whirlpool GH5176XPB2 MICROWAVE OVEN 1.8 Cu. Ft.
Whirlpool GH5176XPQ0 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5176XPQ1 MICROWAVE HOOD COMBO
Whirlpool GH5176XPQ2 MICROWAVE OVEN 1.8 Cu. Ft.
Whirlpool GH5176XPS0 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5176XPS1 MICROWAVE HOOD COMBO
Whirlpool GH5176XPS2 MICROWAVE OVEN 1.8 Cu. Ft.
Whirlpool GH5176XPT0 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5176XPT1 MICROWAVE HOOD COMBO
Whirlpool GH5176XPT2 MICROWAVE OVEN 1.8 Cu. Ft.
Whirlpool GH5184XPB0 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPB1 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPB2 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPB3 MICROWAVE OVEN 1.8 Cu. Ft.
Whirlpool GH5184XPB4 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPB5 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPB6 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPB7 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPQ0 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPQ1 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPQ2 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPQ3 MICROWAVE OVEN 1.8 Cu. Ft.
Whirlpool GH5184XPQ4 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPQ5 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPQ6 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPQ7 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPS0 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPS1 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPS2 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPS3 MICROWAVE OVEN 1.8 Cu. Ft.
Whirlpool GH5184XPS4 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPS5 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPS6 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPS7 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPT0 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPT1 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPT2 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPT3 MICROWAVE OVEN 1.8 Cu. Ft.
Whirlpool GH5184XPT4 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPT5 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPT6 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH5184XPT7 Microwave Oven 1.8 Cu. Ft.
Whirlpool GH6177XPB0 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPB1 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPB2 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPB3 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPB4 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPB5 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPQ0 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPQ1 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPQ2 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPQ3 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPQ4 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPQ5 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPS0 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPS1 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPS2 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPS3 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPS4 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPS5 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPT0 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPT1 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPT2 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPT3 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPT4 MICROWAVE HOOD COMBINATION
Whirlpool GH6177XPT5 MICROWAVE HOOD COMBINATION
Whirlpool GH6178XPB0 MICROWAVE HOOD COMBINATION
Whirlpool GH6178XPB1 MICROWAVE HOOD COMBINATION
Whirlpool GH6178XPB2 MICROWAVE HOOD COMBINATION
Whirlpool GH6178XPQ0 MICROWAVE HOOD COMBINATION
Whirlpool GH6178XPQ1 MICROWAVE HOOD COMBINATION
Whirlpool GH6178XPQ2 MICROWAVE HOOD COMBINATION
Whirlpool GH6178XPS0 MICROWAVE HOOD COMBINATION
Whirlpool GH6178XPS1 MICROWAVE HOOD COMBINATION
Whirlpool GH6178XPS2 MICROWAVE HOOD COMBINATION
Whirlpool GH6178XPT0 MICROWAVE HOOD COMBINATION
Whirlpool GH6178XPT1 MICROWAVE HOOD COMBINATION
Whirlpool GH6178XPT2 MICROWAVE HOOD COMBINATION
Whirlpool GH6208XRB0 MICROWAVE HOOD COMBINATION
Whirlpool GH6208XRQ0 MICROWAVE HOOD COMBINATION
Whirlpool GH6208XRS0 MICROWAVE HOOD COMBINATION
Whirlpool GH7145XFB0 MICROWAVE
Whirlpool GH7145XFB1 MICROWAVE
Whirlpool GH7145XFQ0 MICROWAVE
Whirlpool GH7145XFQ1 MICROWAVE
Whirlpool GH7145XFT0 MICROWAVE
Whirlpool GH7145XFT1 MICROWAVE
Whirlpool GH7145XFZ0 MICROWAVE
Whirlpool GH7145XFZ1 MICROWAVE
Whirlpool GH7155XHS0 MICRO OVEN/HOOD COMBO
Whirlpool GH7155XHS1 MICROWAVE OVEN/HOOD COMBO
Whirlpool GH7155XKB0 MICROWAVE HOOD COMBO
Whirlpool GH7155XKQ0 MICROWAVE HOOD COMBO
Whirlpool GH7155XKT0 MICROWAVE HOOD COMBO
Reply With Quote
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
  #2 (permalink)  
Old 03-06-2008, 08:58 AM
Junior Member
 
Join Date: Mar 2008
Posts: 8
RegB is on a distinguished road
Default

I removed the filter temporarily to eliminate the possibility that it is blocking air flow. This made no difference.
Reply With Quote
  #3 (permalink)  
Old 03-06-2008, 11:36 AM
Junior Member
 
Join Date: Mar 2008
Posts: 8
RegB is on a distinguished road
Default

On the idea that the thermostat might have been failing to hold the fan relay on, I disconnected the thermostat and shorted the red and white wires together. This simulated the original non-programmable round thermostat from 35 years ago, which was basically a mercury switch on a bi-metal coil.
Same symptoms.
Reply With Quote
  #4 (permalink)  
Old 03-08-2008, 11:04 AM
Junior Member
 
Join Date: Mar 2008
Posts: 8
RegB is on a distinguished road
Default

Yesterday I replaced the (combination) fan and limit control.
No change.

Today I tore apart some flue sections to see if there were any blockages, dead squirrels, etc. Not much soot for 35 years, the chimney is also clear.
Still having the same problem.

BTW, are furnace fans usually 1 or 2 speeds ?
Does anyone from appliancepartspro ever read and respond to these questions ?
I was told by the (somewhat rude) live chat person to post here.
The person that answered the phone said basically the same thing, that I would receive a technical answer within 24 hours.
Reply With Quote
  #5 (permalink)  
Old 03-12-2008, 04:02 PM
Junior Member
 
Join Date: Jan 2008
Location: Kentucky
Posts: 8
#1 tech is on a distinguished road
Default

sounds like your motor is interaly bad (thermal overload). most any HVAC store will carry a replacement. be sure to take the old one with to get a correct replacement. if it is heat only then use the low speed. if it is heating and cooling then use low for heat and high for cooling. sorry i did not post sooner getting ready for summer at work
Reply With Quote
  #6 (permalink)  
Old 03-12-2008, 05:39 PM
Junior Member
 
Join Date: Mar 2008
Posts: 8
RegB is on a distinguished road
Default

Quote:
Originally Posted by #1 tech View Post
sounds like your motor is interaly bad (thermal overload). most any HVAC store will carry a replacement. be sure to take the old one with to get a correct replacement. if it is heat only then use the low speed. if it is heating and cooling then use low for heat and high for cooling. sorry i did not post sooner getting ready for summer at work
Thanks for your reply.
It was indeed the fan motor, which I diagnosed without any help from APP.
BTW, are you an appliancepartspro employee ?

For anyone else who gets down this path;
At some point it occurred to me that, but for the new switch, the motor was hooked pretty much directly across 110 VAC. Since I had already replaced that switch ....hmmm, kinda/gotta be the motor, so I did in fact wire it directly across 110 VAC (with the shutdown switch set to OFF) and sure enough I got the same symptoms. The whole lower blower unit is mounted on rails that slide out after removing a couple of small retaining screws. The squirrel cage is mounted to the (1/2 inch diameter) shaft with a set screw to the milled flat, the motor is mounted to the opposite side of the housing with 3 bolts to arms that are held to the motor with a band. All of this is quite intuitive once you have it all out. The 3 arms and retaining band had to be transfered to the new motor, of course I took care to be sure that I got it on STRAIGHT, tight and as close as I could to the same distance from the motor face as it was on the old one. I took the old motor with me and picked what little brain I could find in the local sales counter staff. Well, it came with a schematic anyway. The new motor came with a longer shaft, which didn't matter because it just sticks farther into the fan cavity. I also turned around the 4 thin screws that run through the motor and hold the end plates on, to get their excess length away from the face of the motor where it MIGHT have mattered.

I now (for 2 days) have a very quiet and seemingly efficient heating system. It cycles more evenly, I suspect partly the new motor and partly the cleaning that I did are responsible for this.
About $200 total for switch and motor, the neighbor paid some $5500 to replace his about 5 years ago (same symptoms), but I only found that out yesterday (-:
What to do with the $5300 I saved ?
I'll think of SOMETHING I'm sure, some of it should probably go to converting it to pilotless ignition (hot surface), something I've thought about every few years as the co$t of natural gas has continued to rise.
Reply With Quote
  #7 (permalink)  
Old 03-12-2008, 08:09 PM
Junior Member
 
Join Date: Jan 2008
Location: Kentucky
Posts: 8
#1 tech is on a distinguished road
Default

no i am not ... just a HVAC tech who thought he could help out ... if i was you i would look into changeing your unit over to a newer more effecent unit .. if you look on the ID plate on the furnace it should tell you input and output of you furnace .. judgeing from the age i would say it is no more than 80% .. they now sell 90+ units which you can get to work with a heatpump ... by doing this you can cut your heating costs by a very large amount ... i have seen saveings of 2/3 of the yearly cost .. plus it would add a/c in the summer ... if you would care for ferther advice i would be happy to help ... i also have some plans for a quick and easy solar window box that a person could bulid and helps dramaticly with engery cost
Reply With Quote
  #8 (permalink)  
Old 03-15-2008, 04:53 AM
Junior Member
 
Join Date: Mar 2008
Posts: 8
RegB is on a distinguished road
Default

If I could swap out the burner & ignition system for a higher efficiency unit that would be fine. If I had to replace the whole standing unit that would be impractical. Just getting a new unit in and the old unit out would require the moving of too much "stuff", walls, etc.

I could get 50 or 60 pound sub-assemblies about the size of the blower unit in there without too much trouble, but not a whole cabinet.

If there isn't a "guts replacement/upgrade kit", maybe there should be.
Reply With Quote
  #9 (permalink)  
Old 03-18-2008, 07:52 PM
Junior Member
 
Join Date: Jan 2008
Location: Kentucky
Posts: 8
#1 tech is on a distinguished road
Default

the technology has changed a lot in 35 years. while a deferent burner create more heat. The heat exchanger would not transfer it to the air. A good contractor should be able to disassemble the unit in place. Also you will more than likely find the new models to be smaller in size. Here is a link Alpine Home Air Products: Contractor-grade heating, air conditioning and indoor-air quality products at wholesale prices. ... you can match out the output of your furnace. They have dimensions and you can see if it will fit. Remember 20% of your heating bill is not being used. If you lowered that by 15% how much would that save you next year .. the year after ... in 5 years ... i saw gas at $3.39 yesterday .. sorry i will get off my soap box
Reply With Quote
  #10 (permalink)  
Old 04-02-2014, 07:04 PM
Junior Member
 
Join Date: Mar 2008
Posts: 8
RegB is on a distinguished road
Default

Quote:
Originally Posted by christina_williams View Post
Hi.. Proper & regular maintenance is a must to keep your furnace in proper working order. Monthly replacement of the filter in your furnace is one of the most important things you can do to extend the life and efficiency of your furnace. So, for this you have to go for a professional Furnace Repair service provider.
REALLY ?
Six YEARS later and all you can contribute is the standard noise from the generic owners manual ?

It worked FINE for 35 years, WITHOUT any so called "service"
a PART wore out, it was replaced,
it has worked FINE for 6 more years, WITHOUT further so called "service".

Evidently I do NOT need a "Professional Furnace Repair Service" - and I seriously doubt that many other people do either.

A SIMPLE, a VERY simple DIY repair of a household item.
"Professional furnace repair service provider" indeed.
Reply With Quote
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
intermittent furnace problem depa007 Heating, Ventilation, and Air Conditioning (HVAC) 0 12-10-2009 02:28 PM
furnace roel Heating, Ventilation, and Air Conditioning (HVAC) 1 10-05-2009 08:28 PM
Furnace motor capacitor problem fixed! franky Heating, Ventilation, and Air Conditioning (HVAC) 0 07-18-2009 01:55 PM
furnace problem!!!! jeremy69 Heating, Ventilation, and Air Conditioning (HVAC) 2 02-07-2009 04:07 PM



All times are GMT -7. The time now is 09:11 AM.

The content on this web site is for informational purposes only and is not intended to replace an on-site diagnosis from a qualified appliance service technician. By reading any content on this site you agree to AppliancePartsPros.com , Inc. disclaimer and Terms of Use.
Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO ©2011, Crawlability, Inc.

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17