Model Number: DFS2A Brand: -other- Age: 1 - 5 years
Hi, i own an international comfort products AC system (duct free systems)
The evaporator his always freezing. I tought the calibrated orifice might be clogg (chunk of welding). I need your help to know exactly where it should be located. thank you Related Models |
|
See inside of your appliance - diagrams and part photos for virtually every model. powered by AppliancePartsPros.com |
|
|||
|
You are probably running the unit at a low outdoor temperature. This will prevent the condenser from condensing properly. As a result the refrigerant is pooling up in the condenser and starving the evaporator which results in lower pressure. Lower pressure results in lower temperature hence the coil freeze up.
|
|
|||
|
That was on another forum. Please list all conditions such as evaporator coil (clean thoroughly), condenser coil (clean thoroughly) filters changed, supply air temperature, return air temperature, dry bulb temperature, wet bulb temperature. Since this is a fixed orifice the charge is verified by super-heat, so post that reading as well.
Last edited by icehouse : 06-01-2009 at 10:23 AM. |
|
|||
|
Use the following:
|
|
|||
|
outside temperature 90 F with 20 % humidity
high Low 165 40 150 25 150 23 (psi) Temperature external of evaporator 49.5F at 23 psi (shoud be -2F) Temperature external of condenser 97 F at the fan at 150 psi (shoud be -82.5F) Fitting at the condenser are full of ice and evaporator his starting to fill up too. Thank you |
|
|||
|
Pressures are way off for R22. Head Pressure should be around 275# (110*F condensing temperature).
Suction 68# (40*F evaporator temperature) |
|
|||
|
Also read:
|
|
See inside of your appliance - diagrams and part photos for virtually every model. powered by AppliancePartsPros.com |
| Thread Tools | Search this Thread |
| Display Modes | |
|
|
|
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| what is diffrent between LP gs orifice and Netural gas orifice | mani | Oven Repair (including Ranges and Cooktops) | 0 | 04-30-2009 06:31 AM |
| whirlpool orifice for LP | sprasad | Dryer Repair | 2 | 04-05-2009 09:12 AM |
| Natural Gas Orifice | jeff glanzer | Oven Repair (including Ranges and Cooktops) | 1 | 12-27-2008 09:13 PM |
| Orifice Tube Assembly | REYNA_CERRATRO123@MSN.COM | Oven Repair (including Ranges and Cooktops) | 0 | 10-16-2008 10:49 AM |
| changed out both orifice tube assemblies, burning tall and yellow now | gene1340 | Oven Repair (including Ranges and Cooktops) | 0 | 07-02-2008 09:12 AM |