I have a Amana 90 Air Command, it is leaking water, which is dripping out from the seal behind the

..."
 
 
Register | FAQ's | New Posts | Today's Posts | Extras
Appliance Repair Forum > Appliance Repair Help > Heating, Ventilation, and Air Conditioning (HVAC) » Water Leak behind blower motor

Post New Thread  Reply By reading any content on this site you agree to AppliancePartsPros.com, Inc. disclaimer and Terms of Use.
 
LinkBack Thread Tools Search this Thread Display Modes
  #1 (permalink)  
Old 12-09-2008, 05:46 PM
fxwg98 fxwg98 is offline
Junior Member
 
Join Date: Dec 2008
Posts: 1
fxwg98 is on a distinguished road
Default Water Leak behind blower motor
Model Number: 7724-02-2020   Brand: Amana   Age: 1 - 5 years   

Appliance Parts from AppliancePartPros.com
I have a Amana 90 Air Command, it is leaking water, which is dripping out from the seal behind the blower. I've checked & blown out both exhaust and air supply lines (leading outside), check the humidifer (which is draining like it is required to) and checked the line coming from the unit behind the blowed, they drain into a floor drain. Does anybody have diagram or cut away showing what the inside of the blower unit looks like. Any help would be appreciated, thank you.

Related Models
Amana 773.000 Range - S/c S/i Ddraft Gas
Amana 776.000 Range - S/c S/i Ddraft Gas
Maytag 77C Dryer - Gas
Magic Chef 77E-5CXWM9 Walloven - S/c Mwave Ele
Magic Chef 77E-5EXWW Walloven - S/c Ele
Magic Chef 77EN-5CXWM9 Walloven - S/c Mwave Ele
Magic Chef 77EN-5EXWW Walloven - S/c Ele
Magic Chef 77F-5EVWM 
Magic Chef 77F-5EVWW 
Magic Chef 77F-5EXWM 
Magic Chef 77F-5EXWM9 
Magic Chef 77F-5EXWW 
Magic Chef 77FA-5EVWM 
Magic Chef 77FA-5EVWW 
Magic Chef 77FA-5EXWM 
Magic Chef 77FA-5EXWW 
Magic Chef 77FK-5EVWM 
Magic Chef 77FK-5EVWW 
Magic Chef 77FK-5EXWM Walloven - S/c Mwave Ele
Magic Chef 77FK-5EXWW Walloven - S/c Ele
Magic Chef 77FN-5EVWM Walloven - S/c Mwave Ele
Magic Chef 77FN-5EVWW Walloven - S/c Ele
Magic Chef 77FN-5EXWM 
Magic Chef 77FN-5EXWM9 Walloven - S/c Mwave Ele
Magic Chef 77FN-5EXWW 
Magic Chef 77J-5EXWM 
Magic Chef 77JK-5EXWM Walloven - S/c Mwave Ele
Magic Chef 77JN-5EVWM Walloven - S/c Mwave Ele
Magic Chef 7858XRA Walloven - S/c Dbl Oven Ele
Magic Chef 7858XRW Walloven - S/c Dbl Oven Ele
Magic Chef 7858XUA Walloven - S/c Dbl Oven Ele
Magic Chef 7858XUW Walloven - S/c Dbl Oven Ele
Magic Chef 7858XVA Walloven - S/c Dbl Oven Ele
Magic Chef 7858XVW Walloven - S/c Dbl Oven Ele
Frigidaire 787 FRIGIDAIRE DISHWASHER 24"
Magic Chef 7898VAD Range - S/c Mwave Ele
Magic Chef 7898VAV Range - S/c Mwave Ele
Magic Chef 7898VRA Range - S/c Mwave Ele
Magic Chef 7898VRV Range - S/c Mwave Ele
Magic Chef 7898VVV Range - S/c Mwave Ele
Magic Chef 7898XRA Range - S/c Mwave Ele
Magic Chef 7898XRW Range - S/c Mwave Ele
Magic Chef 7898XVA Range - S/c Mwave Ele
Kenmore 790.1  HAIR CLIPPERS
Kenmore 790.2  HAIR CLIPPERS
Kenmore 790.3  HAIR CLIPPERS
Kenmore 790.330020  GAS COOKTOP
Kenmore 790.33002990  GAS COOKTOP
Kenmore 790.33002991  GAS COOKTOP
Kenmore 790.330030  GAS COOKTOP
Kenmore 790.33003990  GAS COOKTOP
Kenmore 790.33003991  GAS COOKTOP
Kenmore 790.330040  GAS COOKTOP
Kenmore 790.33004990  GAS COOKTOP
Kenmore 790.33004991  GAS COOKTOP
Kenmore 790.330090  GAS COOKTOP
Kenmore 790.33009990  GAS COOKTOP
Kenmore 790.33009991  GAS COOKTOP
Kenmore 790.330120  GAS COOKTOP
Kenmore 790.33012990  GAS COOKTOP
Kenmore 790.33012991  GAS COOKTOP
Kenmore 790.330130  GAS COOKTOP
Kenmore 790.33013990  GAS COOKTOP
Kenmore 790.33013991  GAS COOKTOP
Kenmore 790.330140  GAS COOKTOP
Kenmore 790.33014990  GAS COOKTOP
Kenmore 790.33014991  GAS COOKTOP
Kenmore 790.330190  GAS COOKTOP
Kenmore 790.33019990  GAS COOKTOP
Kenmore 790.33019991  GAS COOKTOP
Kenmore 790.33022100  GAS COOKTOP
Kenmore 790.33023100  GAS COOKTOP
Kenmore 790.33024100  GAS COOKTOP
Kenmore 790.33029100  GAS COOKTOP
Kenmore 790.33032100  GAS COOKTOP
Kenmore 790.33033100  GAS COOKTOP
Kenmore 790.33034100  GAS COOKTOP
Kenmore 790.33039100  GAS COOKTOP
Kenmore 790.45702300  GAS RANGE
Kenmore 790.45704300  GAS RANGE
Kenmore 790.45709300  GAS RANGE
Kenmore 790.45712100  DUAL FUEL SIDE-IN RANGE
Kenmore 790.45712102  SEARS/GAS RANGE
Kenmore 790.45712103  SEARS/GAS RANGE
Kenmore 790.45714100  DUAL FUEL SIDE-IN RANGE
Kenmore 790.45714102  SEARS/GAS RANGE
Kenmore 790.45714103  SEARS/GAS RANGE
Kenmore 790.45719100  DUAL FUEL SIDE-IN RANGE
Kenmore 790.45719102  SEARS/GAS RANGE
Kenmore 790.45719103  SEARS/GAS RANGE
Kenmore 790.46132300  GAS RANGE
Kenmore 790.46133300  GAS RANGE
Kenmore 790.46134300  GAS RANGE
Kenmore 790.46139300  GAS RANGE
Kenmore 790.468120  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.46812990  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.46812991  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.46812992  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.46812993  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.468130  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.46813990  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.46813991  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.46813992  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.46813993  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.468140  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.46814990  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.46814992  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.46814993  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.468190  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.46819990  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.46819992  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.46819993  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.46832100  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.46832101  SEARS/GAS RANGE
Kenmore 790.46832102  SEARS/GAS RANGE
Kenmore 790.46833100  DUAL FUEL RANGE
Kenmore 790.46833101  SEARS/GAS RANGE
Kenmore 790.46833102  SEARS/GAS RANGE
Kenmore 790.46834100  DUAL FUEL SLIDE-IN RANGE
Kenmore 790.46834101  SEARS/GAS RANGE
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
  #2 (permalink)  
Old 12-14-2008, 05:26 AM
agatto2 agatto2 is offline
Junior Member
 
Join Date: Dec 2008
Posts: 4
agatto2 is on a distinguished road
Default

Their is usually no cutaways around. You might have to pull the blower motor to see where the water is coming from .

I am guessing this is an high efficient furnace. I would start by looking at all the tubing connections, make sure they are in the right place (look at - and read the instruction manual) they all should have clamps on them.

Every thing should be level (or fairly close) .

Make sure the hole in the floor is draining fast enough to take the flow from a humidifier , and a high efficiency furnace. If not ad a condensate pump.

I would also turn off the humidifier to see if the leak stops, more then one time i have had problems with improper installations of humidifiers.

If all that does not work re post ,,, there are a couple other things you might be able to do
__________________
I do what you see from a bus
[URL="http://www.furnacebook.com"]www.furnacebook.com[/URL]
[EMAIL="anthony@furnacebook.com"]anthony@furnacebook.com[/EMAIL]
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #3 (permalink)  
Old 01-07-2009, 08:02 PM
icehouse icehouse is offline
Senior Expert
APP Volunteer
 
Join Date: Sep 2008
Location: Bay Shore, NY
Posts: 363
icehouse is on a distinguished road
Default

You have a "condensing furnace". Check the condensate drain.
__________________
NATE, HVAC Ecellence, NCCER, PHCC Certified Instructor. Vist www.hvacbob.com
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #4 (permalink)  
Old 01-07-2009, 10:53 PM
ernesto1959 ernesto1959 is offline
Junior Member
 
Join Date: Jan 2009
Location: San Gabriel CA.
Posts: 18
ernesto1959 is on a distinguished road
Default what cicle r u running?

if u r using a/c, ??? , may have a restriction in pan/drain line, but if u r using only at this time the furnace , then the humidifier , or water lines may be ur problem.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #5 (permalink)  
Old 01-08-2009, 04:08 AM
icehouse icehouse is offline
Senior Expert
APP Volunteer
 
Join Date: Sep 2008
Location: Bay Shore, NY
Posts: 363
icehouse is on a distinguished road
Default

Quote:
Originally Posted by ernesto1959 View Post
if u r using a/c, ??? , may have a restriction in pan/drain line, but if u r using only at this time the furnace , then the humidifier , or water lines may be ur problem.
Reading is Fundamental. A by-product of combustion in "Condensing Furnaces" is condensation. Read up before posting.
.
__________________
NATE, HVAC Ecellence, NCCER, PHCC Certified Instructor. Vist www.hvacbob.com
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #6 (permalink)  
Old 01-08-2009, 12:44 PM
ernesto1959 ernesto1959 is offline
Junior Member
 
Join Date: Jan 2009
Location: San Gabriel CA.
Posts: 18
ernesto1959 is on a distinguished road
Default Do you know why they called like that?

do you really know?
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #7 (permalink)  
Old 01-08-2009, 12:55 PM
ernesto1959 ernesto1959 is offline
Junior Member
 
Join Date: Jan 2009
Location: San Gabriel CA.
Posts: 18
ernesto1959 is on a distinguished road
Default condensing furnaces

water is formed as product of combustion , but this water is discharged in a diferent line because is to acidic, straigh to the drain , his problem is a flooded air handler ; if he is not using a/c mode during the day, then the only cause is going to be water lines to humidifier. I DO NOT READ , I KNOW........ . TRYING JUST TO HELP.....
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #8 (permalink)  
Old 01-08-2009, 01:30 PM
icehouse icehouse is offline
Senior Expert
APP Volunteer
 
Join Date: Sep 2008
Location: Bay Shore, NY
Posts: 363
icehouse is on a distinguished road
Default

READ: 90+ condensing furnaces are equipped with two drains.
It is the second drain that usually gets clogged causing moisture to accumulate. This will cause leaking.
__________________
NATE, HVAC Ecellence, NCCER, PHCC Certified Instructor. Vist www.hvacbob.com
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
Reply



Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Blower motor for sears furnace dickcollentine Heating, Ventilation, and Air Conditioning (HVAC) 5 12-06-2008 05:59 AM
Blower motor overheats db55047 Heating, Ventilation, and Air Conditioning (HVAC) 10 12-06-2008 05:39 AM
Blower motor is... blown Alcaeus Heating, Ventilation, and Air Conditioning (HVAC) 3 11-02-2008 06:57 AM
Blower motor problem cruisinjohn Oven Repair (including Ranges and Cooktops) 2 10-08-2008 01:07 PM
Blower motor won't work. rbeckner2 Heating, Ventilation, and Air Conditioning (HVAC) 1 02-20-2008 02:45 PM



All times are GMT -7. The time now is 06:00 PM.

The content on this web site is for informational purposes only and is not intended to replace an on-site diagnosis from a qualified appliance service technician. By reading any content on this site you agree to AppliancePartsPros.com , Inc. disclaimer and Terms of Use.
Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
LinkBacks Enabled by vBSEO 3.0.0

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16