Blower motor overheats

 in

Heating, Ventilation, and Air Conditioning (HVAC)

. "

I have a Goodman GMPN 120-5 Furnace that has been in service for 8 yrs. I have been running the

..."
 
 
Register | FAQ's | New Posts | Today's Posts | Extras
Appliance Repair Forum > Appliance Repair Help > Heating, Ventilation, and Air Conditioning (HVAC) » Blower motor overheats

Post New Thread  Reply By reading any content on this site you agree to AppliancePartsPros.com, Inc. disclaimer and Terms of Use.
 
LinkBack Thread Tools Search this Thread Display Modes
  #1 (permalink)  
Old 11-05-2008, 04:47 PM
Junior Member
 
Join Date: Nov 2008
Posts: 4
db55047 is on a distinguished road
Default Blower motor overheats
Model Number: GMPN 120-5   Brand: -other-   Age: 5 - 10 years   

Appliance Parts from AppliancePartPros.com


I have a Goodman GMPN 120-5 Furnace that has been in service for 8 yrs. I have been running the blower 24/7 since installation. About a week ago the blower motor started shutting down on its internal over temp protection. After running, the motor is too hot to touch for more than a second. I have replaced the control board, motor and cap, put in new filter, checked A coils for plugging and they are not. Have let the furnace blower run with air venting below the A coil to be sure it was not loading the motor. Voltage checks out at 120V. The motor pulls about 7.3-7.5 amps on high speed and about 5.0 amps on the two slower speeds. The draw is up to 13 amps on start up. I have checked to ensure, when running, the motor only has one set of windings energized. The new motor is heating just like the original was. Don't know what else to check. Any ideas as to cause? The motor is adouble shaft double blower cage 3/4 HP 3sp 1075 rpm by GE. What are chances the new motor was defective out of the box? I am able to continue heating the house by running the blower on auto so that it only runs during the heat cycle and has time to cool down some between runs but the underlying problem still exists. I have checked and the motor is excessively hot after a relatively short run during a heating cycle.

Thanks Don


Related Models
General Electric GMR02AAMABB Refrigerator
General Electric GMR02AAMAWW Refrigerator
General Electric GMR02BANABB Refrigerator
General Electric GMR02BANAWW Refrigerator
General Electric GMR02BANBBB Refrigerator
General Electric GMR02BANBWW Refrigerator
General Electric GMR02BANCBB Refrigerator
General Electric GMR02BANCWW Refrigerator
General Electric GMR02BANDBB Refrigerator
General Electric GMR02BANDWW Refrigerator
General Electric GMR02BAVABB REFRIGERATOR
General Electric GMR02BAVAWW REFRIGERATOR
General Electric GMR02CANBWW Refrigerator
General Electric GMR03DAMAWW Refrigerator
General Electric GMR04AAMABB Refrigerator
General Electric GMR04AAMAWW Refrigerator
General Electric GMR04AAVABB REFRIGERATOR
General Electric GMR04AAVAWW REFRIGERATOR
General Electric GMR04BANABB Refrigerator
General Electric GMR04BANAWW Refrigerator
General Electric GMR04BANBBB Refrigerator
General Electric GMR04BANBWW Refrigerator
General Electric GMR04BANCBB Refrigerator
General Electric GMR04BANCWW Refrigerator
General Electric GMR04BANDBB Refrigerator
General Electric GMR04BANDWW Refrigerator
General Electric GMR04BANEBB REFRIGERATOR
General Electric GMR04BANEWW REFRIGERATOR
General Electric GMR04BARABS Refrigerator
General Electric GMR04BARBBS Refrigerator
General Electric GMR04BARCBS Refrigerator
General Electric GMR04HANBBS Refrigerator
General Electric GMR04HANCBS Refrigerator
General Electric GMR04HANDBS Refrigerator
General Electric GMR04HASACS Refrigerator
General Electric GMR04HASBCS Refrigerator
General Electric GMR06AAMARWW Refrigerator
General Electric GMR06AAMBRWW Refrigerator
General Electric GMR06AAPBB Refrigerator
General Electric GMR06AAPBBB REFRIGERATOR P SERIES
General Electric GMR06AAPBWW REFRIGERATOR P SERIES
General Electric GMR06AAPWW Refrigerator
General Electric GMR06AAZABB REFRIGERATOR
General Electric GMR06AAZAWW REFRIGERATOR
General Electric GMS10AAMALWW Refrigerator
General Electric GMS10AAMARWW Refrigerator
Frigidaire GMT1670AS0 Frigidaire/washer
Frigidaire GMWS1339CS0 Frigidaire/washer
General Electric GN1S15CBL Uc filtration-carbon
Norge GN31113WAV RANGE- F/S STD GAS
Norge GN3177WUA RANGE- F/S STD GAS
Norge GN3177WUW RANGE- F/S STD GAS
Norge GN3277XUA RANGE- F/S STD GAS
Norge GN3277XUW RANGE- F/S STD GAS
Norge GN3531WUA RANGE- F/S STD ELE
Norge GN3531WUW RANGE- F/S STD ELE
General Electric GNCF02H Home cond
General Electric GNCF04H Home cond
Gibson GNEM30NWMWA ELECTRIC RANGE
Thermador GNG12M COOKTOP
Thermador GNG12MW GRIDDLE
General Electric GNLD681N10BB DISHWASHER
General Electric GNLD681N10SS DISHWASHER
General Electric GNLD681N10WW DISHWASHER
General Electric GNLD681N20BB DISHWASHER
General Electric GNLD681N20SS DISHWASHER
General Electric GNLD681N20WW DISHWASHER
General Electric GNPR40L00 Softners
General Electric GNPR48L00 Softners
General Electric GNRP40L00 Softners
General Electric GNRP48L00 Softners
Admiral GNS20M82 REF - SXS
General Electric GNSF18Z01 Uc filtration-carbon
General Electric GNSF23Z01 Uc filtration-carbon
General Electric GNSF35Z01 Uc filtration-carbon
General Electric GNSF35Z02 Water softeners
General Electric GNSF35Z03 Water softeners
General Electric GNSF35Z04 Softners
General Electric GNSF39A01 Uc filtration-carbon
General Electric GNSF48A01 Uc filtration-carbon
General Electric GNSH45E01 Water softeners
General Electric GNSH45E02 Softners
General Electric GNSH45E03 Softners
General Electric GNSL05CBL Uc filtration-carbon
General Electric GNSL60FBL Wh filt sys
General Electric GNSM48F02 Softners
General Electric GNSM48F03 Softners
General Electric GNSR2090T9WW WASHER
General Electric GNSR3150H0WW Washer
General Electric GNSR3150H1WW WASHER
General Electric GNSR3150H2WW WASHER
General Electric GNSR3150H3WW WASHER
General Electric GNSR3150H4WW WASHER
General Electric GNSR3150H5WW WASHER
General Electric GNSR3150H6WW WASHER
General Electric GNSV25CBL Uc filtration-carbon
General Electric GNSV30CCC Uc filtration-carbon
General Electric GNSV30CWW Uc filtration-carbon
General Electric GNSV70FBL WATER SYSTEMS
General Electric GNSV70FBL01 Wh filt sys
General Electric GNSV75FWW Wh filt sys
General Electric GNSV75WW01 Wh filt sys
Admiral GNT15M42 REF - TOP MOUNT
Admiral GNT15M42 REF - TOP MOUNT
Admiral GNT15M42 REF - TOP MOUNT
Admiral GNT15M42 REF - TOP MOUNT
Admiral GNT15M42A REF - TOP MOUNT
Admiral GNT15M42L REF - TOP MOUNT
Admiral GNT15M42L REF - TOP MOUNT
Admiral GNT15M4XA REF - TOP MOUNT
Admiral GNT15M4XH REF - TOP MOUNT
Admiral GNT15M4XH REF - TOP MOUNT
Admiral GNT15M82 REF - TOP MOUNT
Admiral GNT15M82 REF - TOP MOUNT
Admiral GNT17M42 REF - TOP MOUNT
Admiral GNT17M42 REF - TOP MOUNT
Admiral GNT17M42 REF - TOP MOUNT
Admiral GNT17M42 REF - TOP MOUNT
Admiral GNT17M4XA REF - TOP MOUNT
Admiral GNT17M4XH REF - TOP MOUNT
Reply With Quote
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
  #2 (permalink)  
Old 11-06-2008, 01:52 PM
Senior Expert
APP Volunteer
 
Join Date: Sep 2008
Location: Bay Shore, NY
Posts: 440
icehouse is on a distinguished road
Default

Quote:
Originally Posted by db55047 View Post
I have a Goodman GMPN 120-5 Furnace that has been in service for 8 yrs. I have been running the blower 24/7 since installation. About a week ago the blower motor started shutting down on its internal over temp protection. After running, the motor is too hot to touch for more than a second. I have replaced the control board, motor and cap, put in new filter, checked A coils for plugging and they are not. Have let the furnace blower run with air venting below the A coil to be sure it was not loading the motor. Voltage checks out at 120V. The motor pulls about 7.3-7.5 amps on high speed and about 5.0 amps on the two slower speeds. The draw is up to 13 amps on start up. I have checked to ensure, when running, the motor only has one set of windings energized. The new motor is heating just like the original was. Don't know what else to check. Any ideas as to cause? The motor is adouble shaft double blower cage 3/4 HP 3sp 1075 rpm by GE. What are chances the new motor was defective out of the box? I am able to continue heating the house by running the blower on auto so that it only runs during the heat cycle and has time to cool down some between runs but the underlying problem still exists. I have checked and the motor is excessively hot after a relatively short run during a heating cycle.

Thanks Don
Can you give all the numbers from the motor as well as any and all "Goodman" information such as full part numbers,model, serial.
__________________
NATE, HVAC Ecellence, NCCER, PHCC Certified Instructor.
a tragedy has happen to me : http://web.me.com/zenzoidman/Bobice/
Reply With Quote
  #3 (permalink)  
Old 11-06-2008, 04:10 PM
Junior Member
 
Join Date: Nov 2008
Posts: 4
db55047 is on a distinguished road
Default

The furnace is a Goodman GMPN 120-5 serial #9805623032 installed 8-11-98. The blower motor is Goodman part #B13400-22. The motor is a GE Motors 5KCP39MG P876CS 3/4 hp 115 V 9.60 A 1075 rpm 60 hz 1 phase motor with a 15.00 MFD 370 V Cap. The motor is 3 speed.

Don
Reply With Quote
  #4 (permalink)  
Old 11-06-2008, 07:19 PM
Senior Expert
APP Volunteer
 
Join Date: Sep 2008
Location: Bay Shore, NY
Posts: 440
icehouse is on a distinguished road
Default

Waiting for AM. Some friends work with the local Goodman distributor.
__________________
NATE, HVAC Ecellence, NCCER, PHCC Certified Instructor.
a tragedy has happen to me : http://web.me.com/zenzoidman/Bobice/
Reply With Quote
  #5 (permalink)  
Old 11-09-2008, 08:06 AM
Senior Expert
APP Volunteer
 
Join Date: Sep 2008
Location: Bay Shore, NY
Posts: 440
icehouse is on a distinguished road
Default

Some additional questions.
Did you check the fan control center ? Also "Heating" should use a slower speed.
__________________
NATE, HVAC Ecellence, NCCER, PHCC Certified Instructor.
a tragedy has happen to me : http://web.me.com/zenzoidman/Bobice/
Reply With Quote
  #6 (permalink)  
Old 11-09-2008, 09:17 AM
Junior Member
 
Join Date: Nov 2008
Posts: 4
db55047 is on a distinguished road
Default

The control board is new and the blower is on the slowest speed for "Heating". There isn't a really noticable difference between high speed and low speed when the wires are exchanged. What's the procedure to check out an AC CAP to be sure it is good?

Don
Reply With Quote
  #7 (permalink)  
Old 11-09-2008, 10:14 AM
Senior Expert
APP Volunteer
 
Join Date: Sep 2008
Location: Bay Shore, NY
Posts: 440
icehouse is on a distinguished road
Default

Quote:
Originally Posted by db55047 View Post
The control board is new and the blower is on the slowest speed for "Heating". There isn't a really noticable difference between high speed and low speed when the wires are exchanged. What's the procedure to check out an AC CAP to be sure it is good?

Don
I located the service manual for your unit. The wiring is as follows :
Black on motor goes to Cool Terminal on module.
Red on motor goes to Heat Terminal on module.
Blue on motor goes to M 1 Terminal on module.

Capacitor Testing : Place the selector switch to "Ohms' on a Multi Meter.
Next place
Red lead on one terminal and Black lead on the other.
It should rise, and slowly fall.
Rises and stays capacitor is
shorted.
Stays on "zero" capacitor is open.
__________________
NATE, HVAC Ecellence, NCCER, PHCC Certified Instructor.
a tragedy has happen to me : http://web.me.com/zenzoidman/Bobice/
Reply With Quote
  #8 (permalink)  
Old 12-03-2008, 11:55 AM
Junior Member
 
Join Date: Dec 2008
Posts: 1
billvo is on a distinguished road
Default

Check the impeller on the combustion blower shaft.
I had similar headaches, blade is a friction fit on shaft, moves until it contacts inside of housing, then either overheats or shuts off completely. This will shut down the furnace or even prevent it from starting.
I took the fan housing apart and put a dab of epoxy on the shaft and impeller (after many other attempts to stop problem) to keep impeller from working its way to side of housing. this solved the problem.
Reply With Quote
  #9 (permalink)  
Old 12-03-2008, 02:39 PM
Senior Expert
APP Volunteer
 
Join Date: May 2008
Location: Mobile,Al
Posts: 724
SublimeMasterJW is on a distinguished road
Default

put an ammeter across the black wire while running on heat. If you get a reading then the motor is running on high speen in heat. You have a bad relay on the board. Check each speed while the motor is runing. It must be running on one speed at a time.
Reply With Quote
  #10 (permalink)  
Old 12-05-2008, 02:57 PM
Junior Member
 
Join Date: Nov 2008
Posts: 4
db55047 is on a distinguished road
Default

My blower is duel shaft with a cage on each end the cages are locked to a flat on the shaft with a set bolt. The cages are not draging on the housing. The motor is running on the correct speed and does not have power to more than one winding at a time. I have checked this with a clamp on amp meter and by disconnecting the wires for speeds not in use. Motor still heats. I am currently having the blower cycle rather than run continuously and so far am getting by without thermal overload but this is a bandaid and not a cure for the problem. I may replace the motor under warrenty on the off chance that I got a bad one out of the box.

Don
Reply With Quote
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Blower Motor RWKEND Oven Repair (including Ranges and Cooktops) 0 02-18-2010 08:52 AM
Blower Motor neboshone Heating, Ventilation, and Air Conditioning (HVAC) 1 10-03-2009 05:52 AM
Kenmore motor overheats Robinscs Washer Repair 0 02-25-2009 03:43 PM
Washer won't spin, and motor overheats rwstern Washer Repair 3 08-30-2008 10:56 PM
New motor overheats tomted1 Dryer Repair 0 05-26-2008 12:03 PM