Dryer Vent Installed Correct?

 in

Dryer Repair

. "

HI, I am getting an inspection result that this is a dangerous venting and is not correct. States "The dryer's

..."
 
 
Register | FAQ's | New Posts | Today's Posts | Extras
Appliance Repair Forum > Appliance Repair Help > Dryer Repair » Dryer Vent Installed Correct?

Post New Thread  Reply By reading any content on this site you agree to AppliancePartsPros.com, Inc. disclaimer and Terms of Use.
 
LinkBack Thread Tools Search this Thread Display Modes
  #1 (permalink)  
Old 02-07-2018, 02:26 PM
Junior Member
 
Join Date: Feb 2018
Posts: 2
attagirl7878 is on a distinguished road
Default Dryer Vent Installed Correct?
Brand: -other-   Age: 1 - 5 years   

Appliance Parts from AppliancePartPros.com


HI,
I am getting an inspection result that this is a dangerous venting and is not correct. States "The dryer's vent is an improper material. This is a fire hazard."
Can anyone tell me why this is improper and what a correct fix would be.
Thanks!
Kate

Attached Images
File Type: jpg vent.jpg (5.3 KB, 4 views)
File Type: jpg IMG_20180207_120200.jpg (44.2 KB, 3 views)
File Type: jpg IMG_20180207_120155.jpg (34.0 KB, 3 views)

Last edited by attagirl7878 : 02-07-2018 at 02:30 PM.
Reply With Quote
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
  #2 (permalink)  
Old 02-07-2018, 02:53 PM
Senior Member
 
Join Date: Aug 2012
Posts: 235
thorning is on a distinguished road
Default

Looks like you have a vent pipe that is hooked up to the dryer with a flexible section of a plastic type material. A metal flex tube is required. Also Of importance is the fact that the vent tube has several elbows that will cause a restriction very quickly. These need to be eliminated if at all possible or at least reduced in quantity. If you have an installation manual for the dryer it should provide the maximum number of elbows allowed and the maximum length of the tube.
Reply With Quote
  #3 (permalink)  
Old 02-07-2018, 03:00 PM
Junior Member
 
Join Date: Feb 2018
Posts: 2
attagirl7878 is on a distinguished road
Default

Quote:
Originally Posted by thorning View Post
Looks like you have a vent pipe that is hooked up to the dryer with a flexible section of a plastic type material. A metal flex tube is required. Also Of importance is the fact that the vent tube has several elbows that will cause a restriction very quickly. These need to be eliminated if at all possible or at least reduced in quantity. If you have an installation manual for the dryer it should provide the maximum number of elbows allowed and the maximum length of the tube.
Thanks so much!
The elbows, I totally understand.
Can you tell me where you see Plastic type material? I did read about plastic material not being good, but I don't see any. I see Flexible metal type, straight vents, tape and clamps.
Sorry, I'm not sure of the exact names, I'm not even close to a professional. Trying to figure out what to ask for of a repair person.
Thanks!
Reply With Quote
  #4 (permalink)  
Old 02-09-2018, 08:30 AM
Senior Member
 
Join Date: Aug 2012
Posts: 235
thorning is on a distinguished road
Default

The material that comes thru the wall is possibly a plastic type. If in doubt and you dont know use a magnet to check it.
Reply With Quote
  #5 (permalink)  
Old 02-09-2018, 03:51 PM
ThatGuy's Avatar
Expert
APP Volunteer
 
Join Date: Jul 2010
Location: middle of nowhere Nebraska
Posts: 1,297
ThatGuy is on a distinguished road
Default

Quote:
Originally Posted by thorning View Post
The material that comes thru the wall is possibly a plastic type. If in doubt and you dont know use a magnet to check it.
That's a worthless test.

If its aluminum the magnet won't stick either.


The problem with the old vent is too many 90 degree elbows. Each 90 degree elbow is equal to 5 feet of straight 4 inch vent.

So in the vent coming out of the wall there are 3 - 90 degrees and a 45 degree. That's the equivalent of nearly 20 feet of vent and you haven't even gone anywhere.

It could be replaced by 1 - 90 and a 45 degree elbow. That would help a lot with air flow.

I'd stick with solid 4 inch vent where possible and use 4 inch flexible aluminum where nothing else will work. Aluminum foil tape works well at sealing the vent.

Use 45 degree elbows whenever you can.
Reply With Quote
  #6 (permalink)  
Old 02-12-2018, 11:46 AM
Senior Member
 
Join Date: Jun 2014
Location: Florida
Posts: 766
brobriffin is on a distinguished road
Default

To answer the question ref "improper material"
The flex hose you have going through the wall, whether its aluminized paper or vinyl (plastic) ducting is not to code. You must use either a rigid or semi rigid ducting through the wall and it should be sealed on both sides. No gaps between the opening and ducting. You should also shorten the rigid ducting to meet the wall transition evenly.
Also as the others have stated reference the total ducting run (inclusive of elbows factor) QUOTE:
"The maximum length of a clothes dryer exhaust duct shall not exceed 25 feet (7,620 mm) from the dryer location to the wall or roof termination."
Otherwise you will need to install a vent booster.
Reply With Quote
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
New heating element installed, still no hot water or dryer swak6287 Dishwasher Repair 0 02-16-2016 10:39 AM
Installed new motor dryer still buzzing Intermittently markbousho Dryer Repair 0 01-19-2015 10:08 AM
Roper dryer will not heat (new parts installed too) xenomorphlv426 Dryer Repair 1 02-03-2014 03:48 AM
New Motor Installed & Now Dryer Will Not Start tbeaun Dryer Repair 1 10-03-2011 04:38 AM
Verify Correct Diagnosis so I can order correct parts JDW123 Dryer Repair 0 07-16-2010 02:59 PM



All times are GMT -7. The time now is 07:27 AM.

The content on this web site is for informational purposes only and is not intended to replace an on-site diagnosis from a qualified appliance service technician. By reading any content on this site you agree to AppliancePartsPros.com , Inc. disclaimer and Terms of Use.
Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2018, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO ©2011, Crawlability, Inc.

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17