You may still have a problem with the wiring if this is a 3 wire hookup.
Here is the wiring diagram for this unit.
http://manuals.frigidaire.com/prodin...0ts_wd_EFS.pdf
Here is the install sheet
http://manuals.frigidaire.com/prodin...34734400es.pdf
In a 3 wire hook up the Neutral (white) and the earth ground are the same wire.
So if the machine frame is not connected and a live wire (black or red) should short to the frame the frame becomes live. Touch it and a ground and you will get a shock.
This does not apply to a 4 wire hook up as Neutral and earth ground (green) are separate. so the green goes to the frame and the Neutral is not connected to the frame.
I would check that it is wired correctly.