When I took off the inspection cover, the copper coils on the ends had condensation, but nothing on the fins at all... Maybe it needs a shot of freon... guess I will have her call for a check-up.

Originally Posted by Simon / APP Team View Post

While the AC is running pull the black wire off the control board (be very careful not to brake or short anything). If the blower stops - it's OK.

There are other things to check: first of all the freon pressure, the air filter. If you don't have the gauges touch the thick copper pipe - must be sweating and dripping condensation. If it's not - there is the sealed system problem.

When testing keep the FAU closed.

Thank you.