When I took off the inspection cover, the copper coils on the ends had condensation, but nothing on the fins at all... Maybe it needs a shot of freon... guess I will have her call for a check-up.
Thanks!

Quote:
Originally Posted by Simon / APP Team View Post
Hi.

While the AC is running pull the black wire off the control board (be very careful not to brake or short anything). If the blower stops - it's OK.

There are other things to check: first of all the freon pressure, the air filter. If you don't have the gauges touch the thick copper pipe - must be sweating and dripping condensation. If it's not - there is the sealed system problem.

When testing keep the FAU closed.

Thank you.

Simon.