Thread: Compressor
View Single Post
  #2 (permalink)  
Old 04-26-2011, 12:18 PM
icehouse icehouse is offline
Senior Expert
APP Volunteer
 
Join Date: Sep 2008
Location: Bay Shore, NY
Posts: 440
icehouse is on a distinguished road
Default

Quote:
Originally Posted by davidderrickson View Post
My compressor (2006 Bryant) outside will not come when I set the thermostat lower then the room temperature.

I replace the contact switch as a guess but still doesn't work.

I can manually start the compressor (will cool the house) by pushing in the contact switch but once I let go the switch comes back out.

Question is: why is the contact switch no being tripped? Is it the capacitor or the circuit board?

Thanks
The low voltage circuit energizes(closes) the contactor.
This is done when the thermostat calls for cooling the coil of the contactor is what causes it to close.
Possibleities are bad thermostat or bad step-down transformer.(220v-24v)
__________________
NATE, HVAC Ecellence, NCCER, PHCC Certified Instructor.
a tragedy has happen to me : http://web.me.com/zenzoidman/Bobice/
Reply With Quote
 