You have 3 pin (triangle) you have to check with a Ohm meter how to check:

Common : Is the biggest resistance
Start: Medium
Run: Smallest

If you see that all of them are almost the same it means shorted or if you touch one of those pins with a pipe & you have a continuity it means its shorted 2.

Hope it was Helpful!
Start is the largest resistance, not Common.
The total resistance between Run and Start should equal the sum of Start to Common and Run to Common.
Example: C to S = 5 Ohms, C to R = 2 Ohms, Then C to S = 7 Ohms
Testing for Grounds: Using an Ohmmeter place one probe on a good ground
such as the ground screw on the compressor. The other probe should then be placed on one of the pins as so stated. If you get a reading, the compressor is grounded.
Testing for open windings: Using an Ohmmeter take the leads and test between any two pins. Reading infinity compressor has open windings.
Testing for shorts: Using an Ohmmeter, place the leads between any two pins. Reading zero shorted compressor.
So much for "Compressors 101"