Suspect, Transformer
In my experience this problem is most likely the low voltage transformer located primarily in the furnace. when the transformer is shorted the fan relay will close on hgh speed and will provide heating when called for by the thermostat but will never provide the 24 volts necesary to change the furnaces motor speed or energize the contactor for the condensing unit, thus no cooling.
|